Hi all

I know this debate has been bounded about the forums in past with various responses.

Usually I measure Zs from the furthest pendant.

However if I use this method during my Elecsa assessment next week, will I be pulled up on unsafe live working practices?

My argument is that within the ceiling rose, the conductors are insulated and terminated within insulated connectors, so, with GS38 probes, presents very little risk of shock

I know the adding up method is acceptable, but don't feel its best practice unless its impractical or unsafe to measure directly.
 
The assessor decides what test you do they usually get you to Zs a socket outlet dont panic
 
In the last 6 years ive not been asked to test a lighting circuit once on inspection

The kewtec adaptors are good though
 
Live testing is a whole different game from "manipulation of live conductors". The latter will get you in trouble, unless you have all the PPE, sufficient knowledge and experience, and a cast iron excuse for HSE as to why you couldn't work dead.

+1 on the Kewtech adaptors - brilliant for the B&Poo lights that people want fitting for next to nothing. You know who you are...

"How much? That's more than the light cost."
"Indeed it is , but I don't live in China. You could get a Chinese electrician, but I suspect the travelling costs would push the price up"
"Mmmmm. I'll think about it and let you know"
 

Reply to Testing Zs on lighting circuit. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
461
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
2K

Similar threads

You would have thought they'd have a switch to flick on and off to engage an override. Not on each PIR but an actual light switch
Replies
5
Views
1K
  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top