On a continuity test on existing lighting circuit, do all bulbs have to be removed, what if there is to many or some can’t be reached.
Trainee Electrician
Trainee Electrician
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Testing in the UK Electrical Forum area at ElectriciansForums.net
no you don't need to remove. you are measuring either R2 or R1+R2. as the bulbs are connected L-N, their resistance will have no effect on your readings.
its just that in college, they said lamps should be remved for R1 R2 testno you don't need to remove. you are measuring either R2 or R1+R2. as the bulbs are connected L-N, their resistance will have no effect on your readings.
ask them why.its just that in college, they said lamps should be remved for R1 R2 test
its just that in college, they said lamps should be remved for R1 R2 test
Yeah you’re right, the tests done in college are for a new installation, looks like with a existing lighting circuit, the lamps don’t need removing .Perhaps they are teaching you how to conduct the series of tests for an installation, not just continuity. In that case, all loads would need to be removed first.
Actually, during initial verification cpc continuity must be verified at all points.During initial verification, r1+r2 or r2 needs to be confirmed at the furthest point. The only way to measure r1+r2 or r2 is physically removing the lamp/cover and gain access to the conductors.
If you are performing r1+r2 this is a good time to confirm polarity too using the light switch.
Just to correct you...…..AND goodwill....etcI do like the way some people like to correct other people in terms. Peace on Earth on Goodwill to all Men etc.
Up yours, just edited itJust to correct you...…..AND goodwill....etc
Have you got an RCD warning label to read?on lR test do the rcds switched to off .