I have recently carries out some testing for a kitchen fitter. He has to submit a test cert to napit... They have sent it back sayin there must be r1+r2 results AND r2 results. I was always lead to believe it was one or the other.
Anyone wiling to enlighten me.
Chris
 
Strictly speaking lower case r1 and lower case r2 results are the resitance values for ring final circuit conductors....

If you've certified a ring final circuit, r1 (line), rn (neutral) and r2 (CPC) end to end resistance values need to be noted.

For continuity of the circuit protective conductor you can eith use the R1+R2 method or R2 method. Whichever you don't use, simply put an 'N/A' in the box and ask them why they want both results!
 
I have recently carries out some testing for a kitchen fitter. He has to submit a test cert to napit... They have sent it back sayin there must be r1+r2 results AND r2 results. I was always lead to believe it was one or the other.
Anyone wiling to enlighten me.
Chris

If the inspector identifies parallel paths that can't be easily cured - then a simple tick can surfice in either box. So it doesn't have to be one or the other, it can be neither and just a simple tick instead of results. But, usually it's one or the other...more often that not the R1+R2 instead of R2.

Never test other peoples work - it lands you in the sh!t if he's wired something wrong.

If this kitchen fitter is such an electrician why doesn't he get himself on the 2395 course? Either that, or he shouldn't be touching the electrics in the first place.
 
Thanks for your replies.
I don't test his work. Basically he installs kitchens for b&q. I do the electrical work. This is the 1st job i've done for him. But it's b&q who insist on a test certificate being sent to napit for check basically. I'm with elecsa myself. It's a load of tedious nonsense but got to do what we've got to do (unfortunately)
Thanks again!
 
R1+R2 or R2 for Radial circuits
r1,rn,r2 and R1+R2 for ring final circuits

they talking out there behind
show then GN3 and a copy of generic schedule of test results

and as your with Elecsa then its nothing to do with napit you jsut have to notify through your scheme
you dont send copies to elecsa so why should they have one lol
the original is given to customer and or a copy to client and you retain a copy thats it charge if they want a copy sent to napit
 
Thanks for your replies.
I don't test his work. Basically he installs kitchens for b&q. I do the electrical work. This is the 1st job i've done for him. But it's b&q who insist on a test certificate being sent to napit for check basically. I'm with elecsa myself. It's a load of tedious nonsense but got to do what we've got to do (unfortunately)
Thanks again!
That sounds weary and I am confused. If you are with Elecsa, why do you not send YOUR notification to Elecsa? I cannot see why NAPIT get it when it is you doing the work??
 
B&Q approached us a couple of years back offering us regular work to wire up new kitchen installations- apparently NAPIT are the only scam that they will work with, regardless of who you're registered with
 
It's a nightmare. I still have to notify through elecsa and do my own Certs. But the kitchen fitter has to have an affiliation with napit and a cert has to be sent to them. It's a load of bull but works work. I am hoping to speak to them tomorrow and clarify things one way or another. I'll let you all know... I'm sure you'll all wait with baited breath lol
 

Reply to testing in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
438
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K
  • Question
Recently did a job with new building techniques, at least to my experience. Dropped ceiling and metal studs in wals and ceiling. Insulation in...
Replies
3
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top