hi
i have been asked to quote for a job where the owner is doing an extension and wants me to do all new wiring in the new part however he wants to keep the existing wiring the same.
he also wants to change over the cu to a new metal one (mk probably). What tests do people recommend i do on the existing wiring to make sure its all safe and in good condition before i take out the old cu?
thanks
 
At the very least IR each circuit, a good sampling of Zs on each circuit and ring final continuity checks. It's also worth looking in light switches/fittings for a CPC.

Some people insist on a full EICR, but I tend to just satisfy myself there are no major issues to contend with on the day and then do a full round of testing once the board is in.
 
If you find a borrowed neutral on the lighting circuit and the guy does not want his landing wallpaper wrecking what are you going to do?

Put both circuits on the same breaker, with a note saying why.

Have a look out for DIY bodge jobs that have been done in the house previously. Metal faceplates not been earthed etc.
 
Last board I did i ended up putting both light circuits on one breaker on same rcd too. With note on certificate as customer didnt want to do remedial works.
Being there was previously no rcds then this would be seen as an improvement.
The inconvenience factor whilst important is surely less than the safety benefits.
Queried it on the annual visit and the niceic bloke said sometimes it cant be avoided and its the camp site rule, leave it same or better than you found it
 
hi
i have been asked to quote for a job where the owner is doing an extension and wants me to do all new wiring in the new part however he wants to keep the existing wiring the same.
he also wants to change over the cu to a new metal one (mk probably). What tests do people recommend i do on the existing wiring to make sure its all safe and in good condition before i take out the old cu?
thanks
Might be best to read "best practice guide 1 it tells you most of what you need to know.
 
Last board I did i ended up putting both light circuits on one breaker on same rcd too. With note on certificate as customer didnt want to do remedial works.
Being there was previously no rcds then this would be seen as an improvement.
The inconvenience factor whilst important is surely less than the safety benefits.
Queried it on the annual visit and the niceic bloke said sometimes it cant be avoided and its the camp site rule, leave it same or better than you found it
I think we have all done that, I certainly have. At the end of the day NO customer is going to want his decorations pulling apart when the wiring has been sitting there for 30 years with no problem.........
 
hi
i have been asked to quote for a job where the owner is doing an extension and wants me to do all new wiring in the new part however he wants to keep the existing wiring the same.
he also wants to change over the cu to a new metal one (mk probably). What tests do people recommend i do on the existing wiring to make sure its all safe and in good condition before i take out the old cu?
thanks
The best practice guide, advises the installer to recommend to the client that an EICR is carried out prior to the CU change.
 
Isn’t the EICR a bit academic really as you are going to have to test the whole lot anyway to issue the EIC. Just makes sense to look for any existing problems first as already mentioned.
 
Isn’t the EICR a bit academic really as you are going to have to test the whole lot anyway to issue the EIC. Just makes sense to look for any existing problems first as already mentioned.
Was only stating what the Best Practice Guide recommends Alan, you don't have to follow the guide, as it's a recommendation from Electrical Safety First.
 
The rub here is that after the change it needs to all work because it did before, so it would be deemed 'your' fault. You need to be sure with testing as above that a circuit that will trip an RCD after its fitted (and doesn't yet because there isn't one) is highlighted, known about and flagged for repair. It's not always the circuits but consumer goods plugged in, the leaking washer / dishwasher / kettle. These might be defective and nobody knows yet and they'll try to blame you.
 
Oh - forgot something! check for cpc on the damn lighting circuits! that one nearly bit me one time! Also 2.5 with a 1mm cpc (but I think you could c3 the latter after a board change)
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Bedfordshire

Thread Information

Title
Tests to carry out prior to new CU
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
21
Unsolved
--

Advert

Thread statistics

Created
A032701,
Last reply from
telectrix,
Replies
21
Views
2,672

Advert

Back
Top