542.1.201 is interesting.

Time to buy shares in copper! Looks like copper rods to every installation regardless of earthing arrangements unless I'm reading this wrong. Should be fun in a terraced house with no garden!
Thought that might just be for tncs to protect against an open pen conductor
 
I appreciate other threads have been opened on this subject since I opened my own, however I'll post here to try and make me look great :)

Having briefly read through the draft, some of the new regs which I noted (amongst others), were;

411.3.3 RCD for all sockets, risk assessment deleted.

411.3.4 RCD for domestic final circuits for luminaires.

421.7 AFDD's. They seem to be suggesting these device to be used on final circuits, combined with the over current device? And the words 'may be used'.

521.10.202. Precluding the use of non-metallic clips, for cables fixed to exposed surfaces. Which suggests to me, this doesn't include cables in domestic properties above plasterboard ceilings.

542.1.201. Earth rod for everyone! Has attracted lots of comments, requesting clarification
 
I appreciate other threads have been opened on this subject since I opened my own, however I'll post here to try and make me look great :)

Having briefly read through the draft, some of the new regs which I noted (amongst others), were;

411.3.3 RCD for all sockets, risk assessment deleted.

411.3.4 RCD for domestic final circuits for luminaires.

421.7 AFDD's. They seem to be suggesting these device to be used on final circuits, combined with the over current device? And the words 'may be used'.

521.10.202. Precluding the use of non-metallic clips, for cables fixed to exposed surfaces. Which suggests to me, this doesn't include cables in domestic properties above plasterboard ceilings.

542.1.201. Earth rod for everyone! Has attracted lots of comments, requesting clarification
I believe they've also deleted the one item of labelled equipment i.e. socket outlets labelled as say fridge when wiring doesn't require rcd protection for domestic, commercial and industrial installations
 
For us lesser mortals who require pretty pictures, and someone else to explain things to us, Darren & Tony are having a chit chat on the subject, in the next dose of 'The Wire';

'The Wire will be broadcast live on Thursday 6 July at 9am - 10am, and can be accessed on several platforms including your PC, tablet or smartphone!

Hosted by industry experts Darren Staniforth and Alan Wells, this edition of The Wire will cover:

• The proposed changes to BS 7671
• How to contribute to the development of the 18th Edition
• Q&A with an opportunity to submit questions

There will also be an opportunity to send in comments afterwards, for NICEIC and ELECSA to consider and incorporate into a submission to BSI'.
 
411.3.3 RCD for all sockets, risk assessment deleted.

So where we can currently get away with not installing RCD's on RFC's in offices powering computers etc because of nuisance tripping... in the next version of BS7671 this won't be the case?
 
So where we can currently get away with not installing RCD's on RFC's in offices powering computers etc because of nuisance tripping... in the next version of BS7671 this won't be the case?
It's presumably because risk assessments are getting used for purposes like this that they are scrapping the exemption.
 
So install more circuits (on new installs) to limit the amount earth leakage on each RCD.

Or cheat and put RCD sockets on each outlet?

Should be fun.
 
So install more circuits (on new installs) to limit the amount earth leakage on each RCD.

Or cheat and put RCD sockets on each outlet?

Should be fun.

Nice try but unless you went to great trouble and expense with type of cable and installation methods the cables supplying said sockets still require 30ma additional protection.:)
 

Reply to The DPC of the draft 18th edition of BS 7671 in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

O
  • Question
I already calculate maximum demand using energy efficient options, e.g. no it's not 100W per light fitting any more despite what the IET says...
Replies
11
Views
2K
  • Question
Someone posted somewhere that they had done so. 18th edition online courses -...
Replies
24
Views
13K
Deleted member 26818
D
At long last, when I mentioned this about 10 years ago, on another forum, after experiencing chaos and damage to an installation I was looking...
Replies
1
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks