What the admendment to the regs are aimed at is spurs of an existing ring final circuit. If you fitted a single point off the ring without using a FCU then you are duty bound in the regs to make that single point compliant to the regs and therefore fit an RCD to the ring final circuit. Regs 411.3.3 and also 522.6.6
Most sparks that are fitting 2 or 3 extra sockets via a FCU will usually fit a RCD type and so the new sockets will conform to the BS 7671-2008
The amendment to 411.3.3 as now added that on a MIEWC it would be permitted not to fit a RCD as additional protection if the designer deemed that fitting the extra socket/sockets was not a risk to the exisiting installation
The IET have also amended reg 522.6.7 to be called 522.6.102 also covering this. So providing that the disconnection times are met the need for fitting a RCD will not be required. If the Zs is sufficiently low enough to disconnect the protection device then as the designer you are complying with the regs if you don't feel the need to fit a RCD.
It's now our call ................
Most sparks that are fitting 2 or 3 extra sockets via a FCU will usually fit a RCD type and so the new sockets will conform to the BS 7671-2008
The amendment to 411.3.3 as now added that on a MIEWC it would be permitted not to fit a RCD as additional protection if the designer deemed that fitting the extra socket/sockets was not a risk to the exisiting installation
The IET have also amended reg 522.6.7 to be called 522.6.102 also covering this. So providing that the disconnection times are met the need for fitting a RCD will not be required. If the Zs is sufficiently low enough to disconnect the protection device then as the designer you are complying with the regs if you don't feel the need to fit a RCD.
It's now our call ................