I know those old crabtree boards and there death traps ( condemned several of them during a PIR on a hotel in Torquay). Frankly the deputy manager should be up before court.
 
Well apart from working on a live board, drilling and connecting loose cables which is illegal as it was possible to isolate..
the circuit breaker you mentioned could not handle the fault level - old C50s are only rated at 4.5kA - so would not have operated safely anyway.
The design was wrong and the routine PIR should have picked this up. If that board had HRC backup protection, the fault would not have been so great and your injuries may well have been less.
So the company and your super are guilty on two counts, unsafe installation and negligent live working.
HSE will have a field day! I'd hate to be defending.
Mike
 
To all the guys reading this, it is a massive lesson learned, at the end of the day you are your own safety officer and there is no way he should have been working live on that panel, no way!!!
 

Reply to The Mighty 3 Phase Flash in the Electrician Talk | All Countries area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
299
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
282
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
355

Search Electricans Forums by Tags

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

  • exceeding voltage drop
    The cable is way undersized. If the voltage drop is detrimental to the installation I would make...
  • TT advise
    OK My take on the precautions to implement when omitting an up front RCD on a TT system. Tails...
  • SIL vs ATEX
    Good morning all, I have a question for those who are CompEx and SIL aware - I have various Ex...
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top