You're viewing the old forum category for electricians jobs. That's fine and you can reply to threads and contact the person who posted the jobs etc too. But for new electricians jobs post to the new job forums instead; Electricians Available for Work Post Here, People seeking domestic electricians post here, People seeking Commercial or Industrial Electricians post here

Discuss The old one still learning in the Electricians Jobs area at ElectriciansForums.net

This electrician job is going for grabs, please don't post contact details in this area of the forum. Use the forum messaging system instead.
With an r2 of 0.84 that would imply that the neutral reading you got was correct (0.84 / 1.66 = 0.5). So I'd be looking at a fault in the line conductor, most likely a loose connection in one of the accessories.
 
Hi telectrix I understand the cpc would be 1.67x greater due to only 1.5 , so yes like you say 0.5 x1.67 =0.83 .
But totally confused with regards the 1.66 calculation
So like you say the phase and cpc seem fine so neutral problem am I still looking at a bad connection do you think ?
 
Ignore me, listen to Tel, I mis read your line and neutral end to end readings. The r1 seems to be right, as Tel said it's the rN that needs investigating, again a loose connection could quite easily be the cause.

The 1.66 (or 1.67 if you want to round up the recurring figure) comes from the difference in the cross sectional area of the live conductors and cpc. 2.5 (mm2) / 1.5 (mm2) = 1.666666666 (recurring).

So r2 should be 1.66 x greater than r1 (and rN).

Hope that makes sense.
 
yep.might just be a terminal screw a bit loose in a socket. any why the confusion with 1.66? it's the ratio of 1.5/2.5.
 
Ignore me, listen to Tel, I mis read your line and neutral end to end readings. The r1 seems to be right, as Tel said it's the rN that needs investigating, again a loose connection could quite easily be the cause.

The 1.66 (or 1.67 if you want to round up the recurring figure) comes from the difference in the cross sectional area of the live conductors and cpc. 2.5 (mm2) / 1.5 (mm2) = 1.666666666 (recurring).

So r2 should be 1.66 x greater than r1 (and rN).

Hope that makes sense.
you are excused due to the fact that you are in Devon. too much time smuggling booze and hanging pirates.
 
my favorite tipple at my old local was Addlestones cloudy cider on draft. 7%. only 2 of us drank it, but we got through 2 x 10 gallons a week between us. sadly my mate has moved to a better world, having been crushed between a 50ft. canal barge and a lock when pi$$ed.
 
yeah, it's that tricky maths again. 1.6666666666 rounded up to 1 67. was much easier when we had roman numerals. XVIIIIIIIIIIIIIVIII.
 

Reply to The old one still learning in the Electricians Jobs area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
430
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

As the cable itself has had the cpc cut off at both ends I would enter a C3 as it doesn't offer any protection within the cable if accidentally...
Replies
3
Views
342
M
Welcome thanks for posting - I have moved this to the right forum
Replies
1
Views
578

Electricians Jobs, Electricians Mate Jobs and Electrician Apprenticeships

Thanks for visiting ElectriciansForums.net, the worlds largest electrical and electricians community. This area of the website is for those who are looking for electricians jobs, electricians mate jobs, or electrical apprenticeship schemes. We have opened up our website to the world after being UK-only for more than 10 years. We now have jobs posted to the forum for domestic, industrial and commercial electrical work from all over the world. Anybody is welcome to register to our forum for free. You can post jobs you have going, or know of. And you can also post to the forum if you're looking for employment or recruitment. Full or part time. Just let us know the full details of the job you have on offer or are looking for and we'll do the rest.

Also note that we have tiling jobs, and plumbing work too.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top