The above won't eliminate anything if the fault is between neutral and earth.
I need help. This is first time I have done electrical wiring after my 42 year old Electrical Engineering understanding. So please help how I can resolve the issue. I have now done the test as you advised and found one particular circuit in a MCB is having fault. Like if I put some load in there the RCD trips. I need help to understand how to find the cause. Please be considerate as I am new to this DYI thing. I have also noticed the other two MCB's are causing the fault as I previously mentioned. Like RCD trips after few minutes of light switched on. And now I found that those two circuits MAY NOT be faulty at all. I am sauying this because I have also tested with just RCD is on and all three MCB's are off. And still my RCD trips after few minutes. That suggests my incoming power supply wire may have faults. How can I find what is causing this RCD trip while all MCB's are OFF.
 
I need help. I am sauying this because I have also tested with just RCD is on and all three MCB's are off. And still my RCD trips after few minutes. That suggests my incoming power supply wire may have faults. How can I find what is causing this RCD trip while all MCB's are OFF.
You obviously have a neutral earth fault which without the correct test kit will be difficult to find
As a DIY your best option would to completely discoonect all the circuits and reconnect them one at a time and switch on the RCD after connecting each one this should find the problem circuit
 
I have not done any test other than continuity and polarity test. Please suggest what other test I need to do and I will try to find details of how to do those.
Follow the eic test result page .start with ring continuity including figure of 8.then choose between phase and earth connected together on al circuits or wonder lead method.r1 +r2 is preferred method for your type of install as it proves polarity.then do your ir test at 500 volts removing all lamps and vulnerable equipment .then start your live testing .loop impedance, rcd test at 30ma on type a setting .preceeeding this you would be carrying out the same tests for supply to dB maybe not rcd test if armoured supply.you will need a mft for this but it will NAIL down fault.no pun intended .
 

Reply to The RCD is tripping after few minutes of the light is on. in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
503
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
2K

Similar threads

Exactly. I was going to ask on the earthing once he clears this boiler fault (suspect on internal component). OP mentions oil boiler but makes no...
2
Replies
19
Views
583
Ok I’ll try this when I’m down
Replies
4
Views
421

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top