I have done the new wiring in my garage with a new distribution box having a RCD and 4 MCB's. And now when I switch a light on, it works for 5 to 10 minutes and then suddenly RCD trips. Please advice what I can do to find the fault. Many thanks.
 
Last edited by a moderator:
I have done the new wiring in my garage with a new distribution box having a RCD and 4 MCB's. And now when I switch a light on, it works for 5 to 10 minutes and then suddenly RCD trips. Please advice what I can do to find the fault. Many thanks.

Could you post your test results - we may be able spot something.
 
Switch off the three MCB's that do not supply the light, if after a time the RCD still trips then its a fault on the lighting circuit or unlikely a faulty RCD, if it does not trip then switch on another MCB and wait a while, if again the RCD does not trip, then repeat the same on the last MCB, this should identify the faulty circuit, in reality I would replace the MCB's with RCBO's this will isolate the fault to one circuit automatically and allow further investigation of that one circuit without cross faults causing confusion.
 
Switch off the three MCB's that do not supply the light, if after a time the RCD still trips then its a fault on the lighting circuit or unlikely a faulty RCD, if it does not trip then switch on another MCB and wait a while, if again the RCD does not trip, then repeat the same on the last MCB, this should identify the faulty circuit,

The above won't eliminate anything if the fault is between neutral and earth.
 
in reality I would replace the MCB's with RCBO's this will isolate the fault to one circuit automatically and allow further investigation of that one circuit without cross faults causing confusion.
That would only be true if the rcbos were DP type ones.
 
Last edited:
OP, what testing has been done? Either during installation or for fault finding? What MFT do you have?

If you give us a bit more info we may be able to help.

Or is this a full DIY install with no testing?
 
What misinformation, if the fault is on the phase side the information given is correct, read the first post, the RCD is tripping.
 
Last edited:
What misinformation, if the fault is on the phase side the information given is correct.
You gave a definitive answer that they could isolate the faulty circuit by turning off the mcb which isn’t correct.

You then said that it could be disconnected automatically by using an rcbo that’s not correct either as the N to E fault will still exist for SP type rcbos.



It wasn’t a criticism it was being helpful to the OP as your post stood it could serve only to cause the OP confusion thinking that the fault had been isolated.

I would also add that the proper way would be to disconnect and test the circuits rather than the way you suggested.

If the OP hasn’t a test meter I suggest getting one and preferably in the hands of a competent electrician.
 
Last edited:
Read the first post, the OP is DIY and it's the RCD tripping so not an N to E fault.

The OP has just wired his garage and installed a new DB. There are any number of potential issues and I don't believe it's wise to provide much in the way of advice until we have more detail from them.

I'm not sure how you think an RCD works, but detecting an imbalance between line and neutral most definitely includes a neutral to earth fault.
 
The above won't eliminate anything if the fault is between neutral and earth.
I need help. This is first time I have done electrical wiring after my 42 year old Electrical Engineering understanding. So please help how I can resolve the issue. I have now done the test as you advised and found one particular circuit in a MCB is having fault. Like if I put some load in there the RCD trips. I need help to understand how to find the cause. Please be considerate as I am new to this DYI thing. I have also noticed the other two MCB's are causing the fault as I previously mentioned. Like RCD trips after few minutes of light switched on. And now I found that those two circuits MAY NOT be faulty at all. I am sauying this because I have also tested with just RCD is on and all three MCB's are off. And still my RCD trips after few minutes. That suggests my incoming power supply wire may have faults. How can I find what is causing this RCD trip while all MCB's are OFF.
 
I need help. I am sauying this because I have also tested with just RCD is on and all three MCB's are off. And still my RCD trips after few minutes. That suggests my incoming power supply wire may have faults. How can I find what is causing this RCD trip while all MCB's are OFF.
You obviously have a neutral earth fault which without the correct test kit will be difficult to find
As a DIY your best option would to completely discoonect all the circuits and reconnect them one at a time and switch on the RCD after connecting each one this should find the problem circuit
 

Reply to The RCD is tripping after few minutes of the light is on. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Ok I’ll try this when I’m down
Replies
4
Views
256
In my opinion replacing the consumer unit and waiting to see which RCBO trips is not a good fault finding technique. If the lighting circuit...
Replies
8
Views
435
davesparks
D
  • Question
Thank you for taking the time to help explain this - much appreciated
Replies
7
Views
663
Which rcd is it? Is it one for everything, one for a few circuits?
Replies
5
Views
335
  • Question
A kettle boiling fish - thats your fault right there... or is it a red herring? :)
Replies
4
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks