In the US, the ring circuit is a totally different concept to me, everything is wired radial.
As I investigated this, it seems it's used to insure proper voltage & amperage depending on where the home is located in proximity to a power station.
Am, I correct?
Stateside, using a ring circuit, the issue would be to make sure it's connected back to the correct leg @ CU (panel)! If not, that'd be a dead short.
the purpose of a ring is to share the load between both legs. e.g. cable rated at 27A (2.5mm in UK) with a ring circuit it almost doubles the current capacity. at the mid point a 30A load will share current 15A each leg. so cable is not overloaded. at other points on the ring, the sharing is proportional to the respective lengths of each leg. near 1 end, the short leg will carry more current than the longer leg, due to lower resistance.
Not sure if you were addressing my point or not but the separate circuit requirements for a fixed load over 2KW can be found in Annex 55A, Final Circuit Arrangements (Normative), 4th Ed., page 306
In the interests of equality and diversity what about white pudding:D:D
BPM Black Pudding Matters
Scolmore,
static zap,