The Spanish way?

E

electrictiff

Hi All,

I have to wire some mobile homes that will end up in Spain, anyone know how buildings are wired over there and maybe any wholesalers that stock the sockets etc i will need to use?

Any help would be appreciated.

Regards

Mick
 
all radials, shuko sockets, Bonding with 10mm give me more details and i'll help where possible. Lenny or phil might want to move this to Non uk section ?????
 
Last edited by a moderator:
thanks for the swift reply, basically we construct Mobile home bungalows, each home is made in 2 halves and at present we wire Kitchen on one ring then 2 further rings, one for each half of home, similarly with the lights we have 2 circuits, one for each half. We will be exporting to Spain so need to make sure we install the correct wiring and equipment.

Regards

Mick
 
Just put a box each half and leave tails to connect radials would be best. these proper mobile homes yes? ie what equipment in kitchen also zones apply in shower room etc.
I once did some work on an Omar 44x20 and also on some tingdene units....... many moons ago
 
Last edited by a moderator:
Hi, These are indeed proper units. Although each home is bespoke we normally fit in the kitchen: Fridge Freezer, Dishwasher, washing machine, gas hob, gas or electric oven (Some require 6mm) and a hood, heating is normally Combi mains gas and no electric shower.

I will have to brush up on the radial scene :)

Regards

Mick
 
40A general switch to a 25A RCD 30ma
c1= 10A 2x1.5 lighting max lights 30 .... singles inside flex tube 16mm
c2 = 16A 2x2.5mm sockets max 20 sockets ...singles inside flex tube 16mm
c3 = 25A 2x 6mm 2 outlets 1 oven etc ...singles inside flex tube 25mm
c4 = 20A 2 x 4mm 3 outlets boiler, dishwasher, washing machine etc singles inside 20mm flex tube
c5 = 16A 2.2.5mm Bathroom/Kitchen 6 outlets singles inside 20mm flex tub

Bonding 10 mm zones apply in bathrooms so anything else let me know m8
 
Looks like we may have one of the units to build, I have not been furnished with the plans yet so will get the accurate info when i see print :)
 
probably your protection will have an rcd ..and dont be suprised with the incoming cable being 4mm or maybe if you are lucky 6mm ususlly you have to ask for more KW and pay a different rate if you need more power , thats sunny spain .....
 