M

MrsS

I’m about to change an CU with rewireable fuses to one with RCBOs, the reasoning behind this is, only a small CU will fit the space and the property only has 4 circuits
5amp Upstairs Lights
5amp Downstairs Lights
30amp Sockets
30amp Cooker
If I use MCB all circuits are protected by an RCD, therefore all circuits would be interrupted under fault conditions; an RCBO ensures that only the circuit with the fault is interrupted.
I plan to test the installation before removing the old CU and because I will be fitting RCBOs I want to avoid any problems with N-E.
Now I’ll get to the point (typically of a woman to go all around the houses)
Tests are:
Ze and Psc tests
Continuity of protective conductors test ( R1 & R2 test at the furthest of the 2xlight circuit and the cooker circuit, adding it to Ze to get Zs). But how does this test check neutral
Then the end to end testing on the sockets circuit
Followed by the cross over test, I know the reading at each socket should be (R1+Rn)/4 or (R1+R2)/4 (spurs higher)
Then Insulation resistance test on all circuit.
Then Zs test of all circuits
Is there anything else I should do or lookout for to avoid problems with the RCBOs
By the way, Which RCBOs are the best to use.
Feedback Welcome
Many Thanks
 
hi mrs s
to do the continuity of protective conductors
1 link line and cpc at db test between line and cpc at all relevent points if its a lighting circuit test at the ceiling rose between sw/line and cpc record highest as R1+R2 value for the circuit operate switches to confirm polarity whilst carrying out the test
2 if you want to you can also measure L- N by linking line and neutral at DB the tesing at all relevent points between line and neutral this result not recorded and value will be substantially the same if same size conductors are used ie 1mm T/E the line , neutral and cpc will give same results as they have same csa
if 1.5mm T/E used then the line to cpc will be higher than the line to neutral as cpc has a smaller csa
use this test for line to neutral (R1 + RN) when testing radial socket outlets to confirm polarity

Would you really do all this before a CU change?? :)


MrsS, have a read of this : http://www.esc.org.uk/pdfs/business-and-community/electrical-industry/BPG6_09.pdf
 
no mate not before changing cu she was asking how to check the neutral in post 3 and she put
neutral to cpc i was just explaining that its carried out between line and neutral R1+RN and its whats used to check radial socket outlets to confirm polarity and doesnt have to be carried out for lighting circuits
but not neded before a board change
 
Last edited:
Don't understand this method very well



I am not surprised on reading my explanation again!

Interestingly it does make some sort of sense and would identify a circuit that for some reason had its own neutral and another neutral from another circuit which would cause rcd problems. This is not the usual problem though and it was not what i meant to say.
I managed to miss out was that you test between the "live of a circuit and the other" neutrals. As the more usual problem especially with 2-way lighting is that the current returns via another circuit.

If IR testing you need to do it at 250v and obviously light switches should be closed.

The easiest way of doing it is to just take the neutral, of say, upstairs lights out of the neutral bar and then test between the live of that circuit and the remaining neutrals on the bar - you only have to separately test all the neutrals if you get a zero reading. Then do the same for downstairs lights. As i'm sure you know it is most likely to be the lighting if there is a problem and it is a quick way of checking.

Hope that makes it a bit clearer and apologies for the confusing first post :)
 

Reply to The testing required before cu change in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
191
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
1K
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

Did a fuseboard change yesterday from an old wylex board to dual rcd on a TT system with 14ohms ZE and finished pretty late. Went back this...
Replies
0
Views
630
Very technical :D
    • Like
Replies
9
Views
590

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top