I’m about to change an CU with rewireable fuses to one with RCBOs, the reasoning behind this is, only a small CU will fit the space and the property only has 4 circuits
5amp Upstairs Lights
5amp Downstairs Lights
30amp Sockets
30amp Cooker
If I use MCB all circuits are protected by an RCD, therefore all circuits would be interrupted under fault conditions; an RCBO ensures that only the circuit with the fault is interrupted.
I plan to test the installation before removing the old CU and because I will be fitting RCBOs I want to avoid any problems with N-E.
Now I’ll get to the point (typically of a woman to go all around the houses)
Tests are:
Ze and Psc tests
Continuity of protective conductors test ( R1 & R2 test at the furthest of the 2xlight circuit and the cooker circuit, adding it to Ze to get Zs). But how does this test check neutral
Then the end to end testing on the sockets circuit
Followed by the cross over test, I know the reading at each socket should be (R1+Rn)/4 or (R1+R2)/4 (spurs higher)
Then Insulation resistance test on all circuit.
Then Zs test of all circuits
Is there anything else I should do or lookout for to avoid problems with the RCBOs
By the way, Which RCBOs are the best to use.
Feedback Welcome
Many Thanks
The R1&R2 test is for continuity of protective conductors and so neutral isn't included, you could however carry out a test to neutral to assist in polarity check.
I often prefer MK RCBO's
Often when I introduce RCDs to an existing installation I will carry out a continuity test between neutral and cpc, to see if any leakage is already existing.
Another thing i do is carry around with me a plug in RCD unit, which I will try out on any suspect old appliances prior to installation. It isn't guaranteed to pick out problem appliances (RCDs have different sensitivity) but it does Ilustrate to the clients your concern prior to installation.
Many Thanks
[The R1&R2 test is for continuity of protective conductors and so neutral isn't included, you could however carry out a test to neutral to assist in polarity check.]
To complete this test, would I link neutral to cpc at CU just like R1&R2, and what reading should I expect?
Just look up the plug in RCD units, does it indicate if a electrical appliance is faulty.
would a split load consumer unit not suit your purpose?
assuming by post you are new - if so life would be made much easier and cheaper this way.
dont go overboard on initial testing,
ze
ring continuity
basic ir test
Thank you Widdler and Ezzzekiel for the advice
Looked at split load consumer unit first but can’t find one that would fit the space I’ve got to work with, which is measured at
W- 250, D - 120mm & H - 260mm
I am new to the forum, and qualified in June NOT A DIYER TAKING WORK OFF THE GOOD OLD SPARKY AGAIN as Amp David suggested.
Just look for some advice like anyone else.
Many Thanks
The plug in tester should work like a normal RCD and hopefully trip if an individual appliance was giving off sufficient leakage to cause problems upon completion. Suspect appliances can be old fridges, washing machines or PC's etc. This won't account for the quantiy of appliances though, which may when all in operation, build up an amount of leakage sufficient to also trip the RCBO anyway.
As for the neutral, yes you could connect it to CPC at the board. Assuming that you have T&CPC cabling, you could play around with the data to verify readings for comparison. (R1&Rn)/2= R1 or Rn. Therefore R1&R2 should equal (R1x1.67)+R1. Then you will have the figures for R1, Rn & R2.
This is all unnecessary though for current requirements, and so I'm sure others here are probably wondering what the heck I'm talking about.
amazing really the simple things
customer can see it for himself -before you changeover to 30mA protection
and have to explain it :(
err you need to order a skip for all your equipment that worked before i started:D
Separate all your neutrals and IR test (or you could continuity test) between them - (there are 6 different combinations with 4 circuits) If you get a zero on any of them chances are you have a shared neutral and potential problems with your RCBOs. If you do have this problem then at least with a split board, although not ideal, you have the opportunity to put the offending circuits on the same rcd and save taking up floorboards/chopping out walls etc.
Of course do the other tests as well to check for other problems. Good luck :)
Many Thanks
hi mrs s
to do the continuity of protective conductors
1 link line and cpc at db test between line and cpc at all relevent points if its a lighting circuit test at the ceiling rose between sw/line and cpc record highest as R1+R2 value for the circuit operate switches to confirm polarity whilst carrying out the test
2 if you want to you can also measure L- N by linking line and neutral at DB the tesing at all relevent points between line and neutral this result not recorded and value will be substantially the same if same size conductors are used ie 1mm T/E the line , neutral and cpc will give same results as they have same csa
if 1.5mm T/E used then the line to cpc will be higher than the line to neutral as cpc has a smaller csa
use this test for line to neutral (R1 + RN) when testing radial socket outlets to confirm polarity
Hmmm:confused:
MrsS,
pushrod,