When doing cable calcs, particularly the Ci for thermal insulation when calculating It, does the amount of thermal insulation refer to the length of cable that is covered by (any thickness of) insulation, or does it refer to the thickness of the insulation that is applied over (any part of the length of) the installed cable?
 
523.7 refers to the length of cable surrounded by insulation.

I think you mean 523.9 Tel :D

I have been getting confused because 523.9 and table 52.2 specifically refer to the length of cable in the insulation, yet table 4D5 gives CCC for Ref Method 100 (covered by thermal insulation not exceeding 100mm in thickness) values as being almost exactly 0.78 the value of ref method C (table 52.2 gives derating factor of 0.78 for length in insulation of 100mm)
 
Table 52.2 gives the derating factors for the length of cable covered by insulation in comparison to method c, clipped direct.

If you then look at table 4D5, and compare method c with method 103 you will see the ccc differs by exactly 0.5 which relates back 523.9, 3rd paragraph i.e a cable surrounded by insulation for a length of greater than 0.5M should be derated by 0.5x.
 

Reply to Thermal insulation in cable calculations in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
300
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
812
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
869

Similar threads

Check the clearance between the back panel and/or terminal cover that you've removed. Look for small burn marks.
Replies
3
Views
483
I can't help wondering about earthing arrangements and how important aesthetics really are when attempting to make the best of a less than ideal...
2
Replies
21
Views
1K
nicebutdim
N

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top