Customer today said to me can you come change my socket, it's melted because of a faulty old extension lead, she'd already thrown it away so couldnt inspect it but I'd thought I'd do a test to be safe on the circuit.
Ring continuity fine.
But when doing IR tests L-N coming as 0, short circuit. But as I'm inspecting the other sockets with appliances that run every day, fridge, washing machine all fine! At the board old rewireable fuses no RCD. Am I testing wrong? L-E fine and E-N fine. Am I right in saying a short would have taken the fuse or at least shown on another socket?
 
IMO IR test giving 0 between L-N would mean a connected load. Hope you did the test at 230v first and haven't blown up some piece of sensitive equipment using 500v.
 
IMO IR test giving 0 between L-N would mean a connected load. Hope you did the test at 230v first and haven't blown up some piece of sensitive equipment using 500v.

Really? I thought 0 meant a short. This could be my problem. There must be an added soccer somewhere because me and the customer went through the whole kitchen disconnecting loads, and it weren't many.
 
A reading of 0.00 Mega ohms on a tester will indicate a short or a connected load of very low impedance


Lets not forget that 0.01 Mega ohms is still 10,000 ohms
 
Last edited:
A reading of 0.00 Mega ohms on a tester will indicate a short or a connected load of very low impedance


Lets not forget that 0.01 Mega ohms is still 10,000 ohms

Right. That could explain it. Thanks Widdler. I disconnected everything what I thought was in sight but there must be something else connected.
I had a feeling I was doing something wrong because the customer said that the extension lead plug had melted, thinking it points to faulty appliance.
 
One that often catches me out is the Immersion heater. A typical 3 kW household immersion will have a resistance of 17-20ohms, so on an IR test it will appear as a short.
 
Spent nearly 2 hours hours on one job trying to locate a similar fault only to find some bugger had plugged the fridge freezer back in :(
 
Neon!! Mate if you think about it almost anything that's plugged in is going to give you a reading of between 0 and a million ohms....... if you do a low ohm test you'll probably find it's very high (it may even read as 'open circuit' on a low ohm reading). There's always something you miss first time, a neon somewhere, or a phone charger tucked away in a corner. Boiler? Deep freeze in the shed? Could be anything, or indeed it could be a fault.

EDIT: Widdler put it better first time round.......
 
Last edited by a moderator:
And for what it's worth I'd say from the look of your pic it was a definite external fault, but even if not it should be sorted when you replace the s/o.
 
also, check the other side of kitchen walls. not unheard of to spur off kitchen ring through wall to add a socket in another room, save floors up and chasing.
 
Widdler's point is very good remember that your IR tester will round down to zero MΩ any reading less than 5000Ω.

If you ever get a zero MΩ IR reading i would then do a continuity reading and you then get a much better idea of what is going on ie a neon, light or a true dead short. You probs had a high enough resistance to restrict the current to a value that is just not taking out the 3036 in the time that the appliance is on but still high enough to melt the socket.
 
Just a point guys , its so difficult to locate every item plugged in especially on lighting circuits , there is always something plugged in some where you've not spotted , what i do is carry out the IR tests LN initially at 250 volts then if clear repeat the test at 500 volts doing this reduces the risk of equipment damage if there is some thing still plugged in
 
Just a point guys , its so difficult to locate every item plugged in especially on lighting circuits , there is always something plugged in some where you've not spotted , what i do is carry out the IR tests LN initially at 250 volts then if clear repeat the test at 500 volts doing this reduces the risk of equipment damage if there is some thing still plugged in

And that's exactly what I do as well. It's a top tip and it could save you the price of a widescreen.
 

Reply to Think I'm losing my touch. in the Talk Electrician area at ElectriciansForums.net

Similar Threads

  • Solved
There is an article about that here: https://www.cement.org/learn/concrete-technology/durability/corrosion-of-embedded-materials It states...
2
Replies
27
Views
2K
  • Question
Good point James. It would have been nice if the manual had mentioned which of the leads were being used for what though. It simply shows the LNE...
Replies
7
Views
520
  • Question
I had an interesting little job this morning. Three sockets in an extension were not working and haven't worked for quite some time (years). It...
    • Like
    • Winner
Replies
0
Views
587
As a trainee, one of the things I've tried to focus on to deepen my interest in the world of electrics, is the space for creativity. I've...
Replies
0
Views
220
  • Question
There could also be a completely unsuitable junction box embedded within the wall and tiled over or just cables in choc blocks in old accessory...
Replies
6
Views
823

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks