I rather foolishly booked in a fault finding job in a 2 hour slot thinking I could solve it quickly, I couldn't!

It has me confused, although I haven't let myself slow down yet and focus so you guys may point out something obvious.

It is an intermittent tripping MCB on a 32A ring ciruit (sometimes the RCD trips) on a dual RCD board. It trips a number of times each day. This has been going on for perhaps a week. Over the last 2 days 5 sockets have actually stopped working completely even with the power on. The ring feeds the whole house.

r1 = 0.14 Mohm (140,000 ohms)
r2 = 28K ohms (28,000 ohms)
rn = 0.7 ohms

With all sockets connected and the ring split in the CU I get :

Leg 1 = L/N - E 0.01Mohms
Leg 2 = I didn't write down the results but they were >1Mohm.

When I split the ring at one socket the IR results were all >1Mohm when tested in the CU, I didn't test at the split socket.

I think I'm getting confused because of the 5 non working sockets. If a ring is broken (as this is) all sockets should still work. Am I right in thinking there HAS to be 2 faults either side of those non working sockets (assuming they are not all spurred from the same socket) or am I missing something?

Usually, in order to find the break I would split the ring. Reconnect the leg that has continuity with the relevant leg in the CU liven them up and eliminate the working ones, but if there are 2 breaks this wont work, i don't think!

Update... the customer has literally just rang saying he removed a socket and just plastered in the cables a while ago and when he bangs that part of the wall it trips! However, this would be just one fault and would still not stop 5 sockets from working!! o_O :disappointed::anguished::tired:
 
Last edited:
Update....

I returned this morning at 8am. It turns out the customer hadn't hidden a socket in the wall, they had removed a TV wall bracket and plastered over. I cut a hole in the wall (stud wall) where the bracket had been and found this..

[ElectriciansForums.net] This fault has me confused! [ElectriciansForums.net] This fault has me confused!

I fixed the above which cleared the poor IR results and got the 5 non working sockets working, I then started fault finding the broken ring. I'd already quizzed the customer a number of times about any thing they'd done or anything out of the ordinary. 30 mins into the fault finding they remembered they'd had a spark off a redundant fused spur. I opened it up and found a disconnected line and cpc. Connected them up and the ring tested as intact.

Then.... I tested the RCD (as at the beginning it was not tripping when tested which I thought may be due to the fault(s) as this sometimes stops the RCD from working) with all outgoing terminals disconnected (thanks again DS). It was faulty. I put a new one in, all tested fine!

3 major faults! Bloody ell, never had that before. I am now having a half day off so I can sit contentedly with a superior grin on my face whilst sipping my coffee and telling you all about it ?:D
 
Result. There's nothing better than using skill and strategy to solve a problem that started out so obtuse that it was difficult even to describe to begin with.
 

Reply to This fault has me confused! in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
488
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
962
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
901

Similar threads

Exactly. I was going to ask on the earthing once he clears this boiler fault (suspect on internal component). OP mentions oil boiler but makes no...
2
Replies
19
Views
939
Update. Went back today as it was popping the other RCD post move, again intermittently with no real pattern. Typically overnight but not every...
Replies
6
Views
323

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top