So.

Went to test RCD with MFT at the socket. My meter alarmed and said reverse polarity. I then checked the connections, they were correct.

I then put my little plug in tester in and it showed something was wrong but doesn't say what. (Look at picture).

Baffled. I then check polarity at the board and the meter. All good.

I plugged my plug in tester into all sockets in the house. I had the same warning in every socket. This tells me the problem is upstream. But everything seems fine 🤯
 

Attachments

  • 20250314_140525.jpg
    20250314_140525.jpg
    974.8 KB · Views: 65
  • 20250314_140233.jpg
    20250314_140233.jpg
    1.1 MB · Views: 63
  • 20250314_140239.jpg
    20250314_140239.jpg
    1.5 MB · Views: 200
  • 1741962423221309146624533205903.jpg
    1741962423221309146624533205903.jpg
    1.9 MB · Views: 158
I'm rashly assuming that you've checked the incoming tails at the CU aren't reversed?
 
That’s the only bit we can’t visually check…. Meter to cu.

You can trace from the cutout fuse to meter… and from mainswitch to rcd within the board.


From the supply side of the mainswitch, what voltages do you get L-E and N-E?
 
Is it only the sockets or are other circuits affected?
If it's only the sockets I'd be looking for a junction box very close to board.
 
So.

Went to test RCD with MFT at the socket. My meter alarmed and said reverse polarity. I then checked the connections, they were correct.

I then put my little plug in tester in and it showed something was wrong but doesn't say what. (Look at picture).

Baffled. I then check polarity at the board and the meter. All good.

I plugged my plug in tester into all sockets in the house. I had the same warning in every socket. This tells me the problem is upstream. But everything seems fine 🤯
Are the neutral legs going back to the correct neutral bar?
 
This is where a decent long wander lead pays for itself!! However - correctly done fig8 tests should also reveal an issue on an RFC (which I'm again, rashly, assuming is the case?). Use a plug in socket adaptor and a long lead back to the board and simple continuity tests will narrow this down before your cuppa's gone cold.
 
I had a case like this where all the sockets (keyswitch) were wired L-N reverse from the manufacturer (we think).
In this case if polarity is correct at the Consumer Unit a wander lead can be used to check L N E at each socket to the disconnected Consumer Unit cables
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Essex
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Trainee Electrician

Thread Information

Title
This is a good'un!!!!
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
14

Thread Tags

Advert

Thread statistics

Created
danspark12345,
Last reply from
newfutile,
Replies
14
Views
406

Advert

TrueNAS JBOD Storage Server

Back
Top