What’s your thoughts on this supply? Came across it recently and wasn’t sure whether to mention it to DNO as it’s quite old but not sure if it warrants it or not.
Speaking of dno fuses I finally got my isolator fitted today .guy was top notch.he arrived at 9 am on the dot.i said don't bother reconnecting my tails I'm away to change the board. He's been with scottish power for 25 years making a fortune with 2 jobs a day ,although he's experienced so prob does other stuff .not sure what.he never mentioned the cut out seal the previous owners sparky had cut off .this is when a good coffee machine is handy
What’s your thoughts on this supply? Came across it recently and wasn’t sure whether to mention it to DNO as it’s quite old but not sure if it warrants it or not.
Looking at the photo it looks like the main earth is on a 951 clamp on the PILC and given the age and also the uncertainty of whether the service head is live and neutral fused I would be on the phone to the DNO
The last one of those service heads I called the DNO to was 2 fuses and one disintegrated when it was pulled. The DNO guy had to warm it up to open it as the pitch had bubbled up and sealed the cover shut