I'm going out later today to quote for installing a kiln in a customers garage.
He has sent me the specs for the kiln and photos of his consumer unit. He tells me that the only other heavy load item is a 10.8kW shower.
The run from the CU to the garage is approximately 25 metres
The kiln is rated at 50 amp / 11.5kW
The CU is split load RCD with 2x 32 amp ring finals, 2x 6 amp lighting and 1x 40 amp shower circuit.
I think the fuse fairy will need to check the DNO fuse size to see if it will cope with the load
I am thinking 10mm2 T&E or SWA depending on routing of the cable
Not sure whether to install separate CU for the kiln (splitting the incomers with Henley block), need to calculate the loads but think this may be better than potentially overloading the current CU.
What would you recommend for connecting the kiln, I initially thought of a commando socket but have only seen them to up to 32 amp.
Any thoughts would be appreciated.
He has sent me the specs for the kiln and photos of his consumer unit. He tells me that the only other heavy load item is a 10.8kW shower.
The run from the CU to the garage is approximately 25 metres
The kiln is rated at 50 amp / 11.5kW
The CU is split load RCD with 2x 32 amp ring finals, 2x 6 amp lighting and 1x 40 amp shower circuit.
I think the fuse fairy will need to check the DNO fuse size to see if it will cope with the load
I am thinking 10mm2 T&E or SWA depending on routing of the cable
Not sure whether to install separate CU for the kiln (splitting the incomers with Henley block), need to calculate the loads but think this may be better than potentially overloading the current CU.
What would you recommend for connecting the kiln, I initially thought of a commando socket but have only seen them to up to 32 amp.
Any thoughts would be appreciated.