Local funeral place is getting a new mortuary fridge unit, and needs some work done.

The CU, just for the room, is high up in the corner, just above the fridge unit. Stupid place to have it, as you need to crawl over the top of the unit to get to it. 2 foot of crawl space, and my dodgy knee. Great.

Board just needs moved along the wall to above the door, everything in surface pvc trunking on wet wall panelling. No trouble extending circuits.
No room elsewhere to put it. Walls are lined with cabinets and other equipment. Above the door is an improvement, just not an ideal working height.

From what I can see, it’s an old Merlin Gerin board, no rcd.

Ideally, would change the board to all RCBO… but I can’t even tell how many circuits are off this board.
Going in on Saturday to PAT their equipment… so I’ll get up on the fridge for a better look.
 
I’m moving the light at some point as well..
Presumably new LED one?
Switch is getting blanked off, new fridge is wider and will cover. Hoping I can pull cables up into that trunking to joint. (In a box, not joint in trunking)
Still a working switch at other door.
I wondered about that, if going for a movement sensor in the light rather than switch?

I am presuming it is not going to have the 'clients' walking about at night...
Wall is brick, so putting things on other side of wall could be messy.
True, though a masonry/diamond hole saw would allow a neat 2-3" hole to be cut for cables to go therough and you could have trunking running down on the other side to the CU.
 
Don’t want to damage the decor on other side of wall, it’s the Chapel of Rest.

Crawled over the fridge and took cover off.

[ElectriciansForums.net] Thoughts on moving an existing CU


I can see now the wet wall cut around this… so I’ll repurpose as a joint box and run extensions along the 2x2 below.
 
I’m moving the light at some point as well..

Switch is getting blanked off, new fridge is wider and will cover. Hoping I can pull cables up into that trunking to joint. (In a box, not joint in trunking)
Still a working switch at other door.
Wall is brick, so putting things on other side of wall could be messy.


View attachment 108540


First of all find out who fitted the ISO and modules Up Side Down. C2 incorrect install etc.

Is the non-diffuser flori unit the only light source.?? If so you could identify and isolate this radial at the DB and run new within the trunking using metal ties and run in conduit fixed to ceiling via PIR sensor to a 5’ LED IP unit. I say IP as it looks like an industrial chilling area.
 
First of all find out who fitted the ISO and modules Up Side Down. C2 incorrect install etc.

Only ever seen a couple of Merlin Gerin single phase boards, but pretty sure they're intended to be installed this way (as per 3 phase boards). Those I've seen even had the same isolating busbar used on their 3 phase boards.
 
I think the room had been wired before they thought about where the fridge was going.
Maybe the original unit was only one door, 3 drawers… and they’ve upgraded to twice the size, hence blocking access to the board.

Now they’re upgrading again… slightly larger unit. No more capacity, but around 8 inches wider… more insulation maybe??

The old unit is going up to their other premises. A garage where they keep the limos and 200 odd coffins.
Please show us that photo of the DB again.
And remember the ‘working in confined spaces’ H&E1972.

Can’t you organise with the client to do the job once they’ve removed the old unit. Gives you good access then, and run a temporary feed to the new unit placed elsewhere in the room.
I bet your dying to start this job.
 
Thanks for all the replies.

The room wasn’t planned well in the first place, but any fridge unit has to be located here so that there’s room in front for the trolley.

There’s 2 light fittings. He just wants this one spun round as it’s lighting up the top of the unit.
Will change to IP if asked for.

It’s not really classed as a “wet” room, but it just makes it easy to clean the walls.

There is a void down right hand side, due to a floor level pipe box, so might just need to use a few WAGO boxes to extend the circuits, although some are surface trunking and could be easily rewired.

The switch is going to be the problem, as the cables are chased into the brick wall behind the wet wall… and a joint made in this switch would be blocked by the new unit.
I suppose if I use WAGOs, they should be MF.
If there’s a feed at the light, then occupancy sensor or quinetic could be a good shout. I could disconnect the switches entirely.


There must be some point where the fridges aren’t getting used.
They must be made up in situ from panels and all bolted together, which will take some time.
The occupants can’t just be left on the trolley or anything.
 
Thanks for all the replies.

The room wasn’t planned well in the first place, but any fridge unit has to be located here so that there’s room in front for the trolley.

There’s 2 light fittings. He just wants this one spun round as it’s lighting up the top of the unit.
Will change to IP if asked for.

It’s not really classed as a “wet” room, but it just makes it easy to clean the walls.

There is a void down right hand side, due to a floor level pipe box, so might just need to use a few WAGO boxes to extend the circuits, although some are surface trunking and could be easily rewired.

The switch is going to be the problem, as the cables are chased into the brick wall behind the wet wall… and a joint made in this switch would be blocked by the new unit.
I suppose if I use WAGOs, they should be MF.
If there’s a feed at the light, then occupancy sensor or quinetic could be a good shout. I could disconnect the switches entirely.


There must be some point where the fridges aren’t getting used.
They must be made up in situ from panels and all bolted together, which will take some time.
The occupants can’t just be left on the trolley or anything.
I’m presuming that you’ve made your ADMD calculations and know the electrical demand required for this new bigger body fridge unit?
Also the minute you start work YOU become responsible for the circuits and their protection, so RCBO/RCD are a must.

I also include at the design stage an IP EM to assist in the event of a light circuit failure or power cut.
 
I’m presuming that you’ve made your ADMD calculations and know the electrical demand required for this new bigger body fridge unit?
Also the minute you start work YOU become responsible for the circuits and their protection, so RCBO/RCD are a must.

I also include at the design stage an IP EM to assist in the event of a light circuit failure or power cut.
RCBO/RCD is not necessarily a must.
 
RCBO/RCD is not necessarily a must.
I know we can only speculate the job in hand from the info supplied, but when I here that they’ve got wet walls, Non IP light fittings/trunking/ finger operated light and fridge ISO switches, not forgetting a large metal fridge unit, why would you not consider Residual Current protection.??
(Taking into account the spike start of a refrigerator unit). Please advise.
 
Installation methods will often dictate if RCD protection is required for all circuits, I often avoid it where possible.
Absolutely, the Data plate and Install will show the way..!!
But as the lengthy accident report made reference in this report to the Beko fridge failures causing that horrendous fire, and highlighting that there wasn’t any residual imbalance protection installed, (which may have reconsidered any immediate fault), the disaster may have been avoided.
I know there were other issues as well.

We attended, following a garage block fire where a fridge freezer on a B16 caused the fire. The fire brigade report stated that the DB socket feed was still live after the fire was dealt with.

Safety first.
 
As can be seen from the earlier photos, the circuits are not RCD protected, but i know the sockets on the end of the circuits are. (BS7288)
Lighting is not, granted.
I wouldn't want the fridge unit itself tripping out unnecessarily, but noted about the data plate. Im only assuming it requires the same power supply, as the director said it was the same size. I should check that myself.
 

Reply to Thoughts on moving an existing CU in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
361
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
921
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
With what looks like only 5 circuits you can probably put a little 5 way garage consumer unit in there if money is tight
2
Replies
17
Views
2K
Promised a photo…. Remember, this was working…. And they managed to move in without hitting it…
    • Like
Replies
4
Views
362

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top