Hi all

Pretty new to working for self. Got call out yesterday for a ring circuit that kept tripping rcd. I identified the faulty cable which had low 0.05 IR reading L to N. I followed this to where next point should be but on opening circuit found only one cable...not good. On closer inspection of sockets I found that most of them had c.p.c's cut out. I can only imagine previous spark had thought this good idea as a previous earth fault had been tripping rcd. Why he cut them right out though so they are impossible to extend I don't know. Anyhow now having disconnected faulty cable decided best thing I could do to make 2.5 not overloaded was to change 32amp mcb for 20amp problem being the washing machine, boiler and oven all on this circuit I did expect this would trip out but thought at least I've give them some power back temporalily which had been without for 3 days and protected cable from overheating. I advised at time although cooker had no rating on it this is likely to cause trouble with circuit and really needs own circuit and is likely to trip out and that ring really needs to be rewired with at very least a new leg from board. What has surprised me is landlord has phoned me since and rather than mcb tripping what's happening is when the various appliances are on other appliances lose power. Ie washine machine on and boiler stops working, cooker on washine machine stops working. Why would this be the case rather than mcb trip out? Thanks
 
Are you saying that the RFC you were called out to investigate a fault, has no CPC? and yet you left it connected?
Did you carry out any of the testing that is required for RFCs, if so what were the results? would be interesting to see them.
'
 
What's the R1+R2 for the circuit? Possibly volt drop causing undervoltage.
 
Are you saying that the RFC you were called out to investigate a fault, has no CPC? and yet you left it connected?
Did you carry out any of the testing that is required for RFCs, if so what were the results? would be interesting to see them.
'

Pete
I have previously been in this situation and others have advised that no c.p.cs at sockets/appliances is not reason enough to not reenergise circuit. If advised client, noted this clearly on cert and put sticker on DB are you saying I shouldn't of done this and walked away from job without reenegising? Thanks
 
Pete
I have previously been in this situation and others have advised that no c.p.cs at sockets/appliances is not reason enough to not reenergise circuit. If advised client, noted this clearly on cert and put sticker on DB are you saying I shouldn't of done this and walked away from job without reenegising? Thanks

Are you sure that advice wasn't for a lighting circuit? An RFC without a CPC is a lot more dangerous.
 
Pete
I have previously been in this situation and others have advised that no c.p.cs at sockets/appliances is not reason enough to not reenergise circuit. If advised client, noted this clearly on cert and put sticker on DB are you saying I shouldn't of done this and walked away from job without reenegising? Thanks
I have never heard that advice and personally I don't think I would have re-energised sockets with no CPC. Possibly leave them some temporary power or try and connect whichevet socket have an earth as I would consider having no earth dangerous.
 
Pete
I have previously been in this situation and others have advised that no c.p.cs at sockets/appliances is not reason enough to not reenergise circuit. If advised client, noted this clearly on cert and put sticker on DB are you saying I shouldn't of done this and walked away from job without reenegising? Thanks
Yes I am
 
Ok thanks I'll call her and send email confirming this circuit should be powered off an not reenergised until all earthing has been rectified
Go there yourself, disconnect all the RFC conductors at the CU and lock off the CB that was feeding the RFC asking your customer to switch it off is hardly a professional approach, It's your neck on the line mate, make sure 100% all RFC conductors are ditched from the CU.
 

Reply to Thoughts on overloaded radial? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
388
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
971
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Continuity of the suspect cable appears fine all cores, from this I could work out the length of it and it really doesn’t appear looking at the...
Replies
2
Views
356
Seen this where T&E has been fixed with a flat bend of too tight a radius.
2 3
Replies
35
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top