Just carrying out an EICR on a farm (!!) with a number of DBs spread in a fashion more similar to a hand grenade then any logical approach.

This one took my interest the most as from the supplying DB (3PN) the installer has run a 3C SWA from two separate C curve 32A 60898 MCBs. Earthing is TT. This runs into an old 17th RCCB board.

Its not a split load board.

They then have one phase running to a 2mod 32A RCBO which supplies an adjacent building and the other phase to an RCCB which supplies the local equipment within that building.

Lots of thoughts on this but just wondering if others views on this, particularly RCCB/RCBO compatibility when reporting findings......🤔
 
1000017040.jpg
 
Theoretically there is nothing wrong with the supply but that board is a lash up.
 
Not got my Regs book with me right now but shouldn't they have separate neutrals?

Also are they different phases? then is there danger 415v on the cover of this board?
 
Got the book it was Reg 521.7 and in particular 521.8.2 But it does specifically say each final circuit and this isn't a final circuit. So by the looks of it though certainly non standard not against regs.

Certainly would like to see warning notices that the board is fed from two different supplies.
 
The board has one three phase supply.
No as above it's two phases and a neutral on a 3C supply.
The triple pole 60947-3 isolator has been used to disconnect neutral as well as the two phases.

Yes having got the books out I can't see it's actually contrary to any regs. As you state as it's a distribution circuit the separate neutral as per 521.8.2 doesn't preclude this.

Warning notices re 415v (as not immediately obvious) and isolating at two separate sources seems very sensible. Also although no thermal deg, Im conscious the crabtree isn't type tested for that board, although strangely the Eaton RCBO seems an even worse fit (in an Eaton board) either way it's definitely not ipx2 on the vertical face.
 
I am worried by that Crabtree RCCB it doesn't look like it fits well!
No as above it's two phases and a neutral on a 3C supply.
The triple pole 60947-3 isolator has been used to disconnect neutral as well as the two phases.

Yes having got the books out I can't see it's actually contrary to any regs. As you state as it's a distribution circuit the separate neutral as per 521.8.2 doesn't preclude this.

Warning notices re 415v (as not immediately obvious) and isolating at two separate sources seems very sensible. Also although no thermal deg, Im conscious the crabtree isn't type tested for that board, although strangely the Eaton RCBO seems an even worse fit (in an Eaton board) either way it's definitely not ipx2 on the vertical face.
Yes Crabtree RCCB is of concern it doesn't look a great fit.

Agree with Westward homebrew to save money probably.

Not familiar with poly phase supplies but would check it is definitely poly phase because the breakers are separate (wouldn't just trust the cable colours) since neutral size would be unaffected if true poly phase.

Actually thinking this really ought to be fed from a TP breaker for safety?
 

Reply to the thread, titled "Thoughts on this install" which is posted in UK Electrical Forum on Electricians Forums.

Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Daily, weekly or monthly email

Thread starter

Joined
Location
Suffolk
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Trainee Electrician

Thread Information

Title
Thoughts on this install
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
10

Thread Tags

Thread statistics

Created
Mattrain1390,
Last reply from
PS Electrics,
Replies
10
Views
64
Back
Top