sdc8843

Hi Guys,

I have just started with a new company and want to run a couple of things by you all.

1. They only want Minor Works Certs filled out for changing lights in bathrooms and sockets in kitchens. I thought it was work on any circuit in kitchen and bathroom because they are special locations.

2. On a certificate in the box Maximum Zs permitted by BS7671 they want me to record 1667 ohms for any circuit controlled by a RCD rather than the tabulated value in the regs.

What are your thoughts
 
For changing lights sockets etc in special lcation a minor works is fine as long as there is no changes to wiring.
The RCD is an interesting one i would they could possibly be right however i personnally use the tabulated values (@100%) with regards to the overcurrent device.
At the end of the day its down to whoever signs as the Inspection and Testing to decide what values they put.:confused:
 
Hi Guys,

2. On a certificate in the box Maximum Zs permitted by BS7671 they want me to record 1667 ohms for any circuit controlled by a RCD rather than the tabulated value in the regs.

What are your thoughts

This is a tabulated value in the regs. Table 41.5 p 50
 
The correct value is the tabulated value agreed
The fgure of 1667 is for an rcd on a TN system

With a TT system.the earth loop impedance is usually pretty high ,therefore the fault current used to operate the RCd will be low and it dis connects as it should
On a TNC-s system the fault current will be very large and could cause a high enough volt drop that may cause non functioning of the electronics of the RCd, and it may not operate,so cant be relied on for fault protection

Having said that,the person oversigning the certificate takes that responsibility,so just go with his method, then keep in mind why I detest the shortcomings of the Qualified supervisor system nonesense operated by that most electricial industry un friendly creatures the Niceic
 

Reply to Thoughts please in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
285
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
786
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
804

Similar threads

  • Question
If they got a shock then something cannot have been isolated.
Replies
7
Views
1K
Thanks for the reply littlespark. Yes the works have been carried out. Surely it is fraudulent because basically the document is Not...
Replies
2
Views
708

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top