Sorry morp but I must be reading a different post.
First EICR
6mm twin and earth cable for shower connected in a 45amp bs1361 = code 2
Shower not rcd protected = code 3
(Shower no RCD protected by 45 A 1361)
external influences so yes ok for pendant
but code 2 for suppleymentary no , why ? because it is not potentially dangerous irespective of the rcd requirement
so code 3 IMO
Your interpretation of the regs is totally different to mine if you are of the opinion that this is a code 3 and will attain a satisfactory assessment on your report!
First EICR
6mm twin and earth cable for shower connected in a 45amp bs1361 = code 2
Shower not rcd protected = code 3
(Shower no RCD protected by 45 A 1361)
external influences so yes ok for pendant
but code 2 for suppleymentary no , why ? because it is not potentially dangerous irespective of the rcd requirement
so code 3 IMO
Your interpretation of the regs is totally different to mine if you are of the opinion that this is a code 3 and will attain a satisfactory assessment on your report!