Sorry morp but I must be reading a different post.

First EICR
6mm twin and earth cable for shower connected in a 45amp bs1361 = code 2
Shower not rcd protected = code 3


(Shower no RCD protected by 45 A 1361)

external influences so yes ok for pendant
but code 2 for suppleymentary no , why ? because it is not potentially dangerous irespective of the rcd requirement
so code 3 IMO

Your interpretation of the regs is totally different to mine if you are of the opinion that this is a code 3 and will attain a satisfactory assessment on your report!
 
its only the supplementary bit i disagreed with , under the 16th it would not have needed rcd for all circuits , so it only lacks the supplymentary bonding , which i would code 3
under 17th it would require rcd and supplymentary , using ESC guidlines it would be code 2 ,
its easy to forget the content of threads that span time which i have appeared to have done , however i could argue either way as to whether its potentialy dangerous, after all any installation is potentialy dangerous when something goes wrong or has human intervention
 
I will have to agree to disagree Morph.

Supplementary bonding under EEBADS was still required to locations of increased shock risk and failure to istall in my book was and is still a Code 2.

I will stick to GN 8 information re this !

Regards

Tony
 

Reply to thoughts please in the Talk Electrician area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
531
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
982
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
916

Similar threads

Generally it would depend on the circumstances whether the armour is earthed both ends or not, and not just dependent on whether it's 2 or 3 core...
Replies
9
Views
354
As the cable itself has had the cpc cut off at both ends I would enter a C3 as it doesn't offer any protection within the cable if accidentally...
Replies
3
Views
505

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top