This is what you need to replace the rcd switch.
That is a good price. I was going to say you can probably buy just the switch on its own, but depending on your local trade outlet stock/staff levels, that might be the best option.
 
Yeah, my idea would be to find the fault that causes it to trip when water is poured on the stones in the sauna. This sounds like a definite link has been made between this action and the tripping of the RCD, so it needs to be investigated.
Yes, a couple of things to find out, such as did it always do this? (i.e. is a 30mA trip too low for that sort of installation) or has something changed.

It might not be the actual sauna heater of course, it could be that a light in the sauna is letting steam in and causing the earth leak. Maybe someone put in a replacement without suitable IP ration, or maybe it has special seals around them that have degraded with time, etc.?

That is the problem with a single RCB and intermittent trip - they might find it is actually a light circuit or similar that is causing it to trip.

Maybe @Vinnie2020 can get them to run it and make it trip then quicky isolate all the MCBs and see if an insulation tests reveals a leaky circuit before it dries out.
 

Reply to three phase board separation in the Commercial Electrical Advice area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
959
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Has the cover been removed, is it TP bussbar? I fitted one as @oscar21 linked to a few months ago, it was actually a nice board and with the TP...
Replies
5
Views
645
Sooo the client has accepted that we don't want to be fraudulently taking electricity so that worry is out of the picture. But now basically the...
Replies
32
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top