Well, having just joined up i thought id post some of the work i get involved with and what not and generally introduce myself!
Im Jamie, I'm 22, and an industrial/commercial electrician in the southwest.
Generally i get alot of fault finding and reactive installation work to do, and I'm just in the process of going self employed now.
But anyway, i went to a site the other day to carry out a EICR and this is what was awaiting me! A 50a TP-N DB that was mounted next to a garage door and was been leaked on by the roof!
As you can see its a bit of a mess!
Well, it turns out that <3 months ago a large electrical contractor in the area had fitted a new supply to the forklift charger (50a single phase), but didnt have any cable big enough so they doubled up 2x 6mm cables for L,N,E, *rolls eyes*
It also turns out the MCB was upside down, causing mass confusion to the guys on site as it kept tripping out due to only been a "b" type
Earth didnt quite fit in the terminal it seems -
So I isolated the board and made safe and the client agreed to let us install a new fuseboard and sort out the cabling issues!
Found a burnt out lighting circuit then realised this might have something to do with it -
So on with a new DB and enclosure,
I elected for a GRP IP65 enclosure with an eaton TP-N DB inside with all cables + conduits passed through the GRP enclosure with stuffing glands and suitable washers with weather proof glands going into the DB.
New supply for the forklift charger -
Lighting Circuit renewed -
There we have it,
Hopefully they are all up to your exacting standards, and C+C is welcome!
Jamie
Im Jamie, I'm 22, and an industrial/commercial electrician in the southwest.
Generally i get alot of fault finding and reactive installation work to do, and I'm just in the process of going self employed now.
But anyway, i went to a site the other day to carry out a EICR and this is what was awaiting me! A 50a TP-N DB that was mounted next to a garage door and was been leaked on by the roof!
As you can see its a bit of a mess!
Well, it turns out that <3 months ago a large electrical contractor in the area had fitted a new supply to the forklift charger (50a single phase), but didnt have any cable big enough so they doubled up 2x 6mm cables for L,N,E, *rolls eyes*
It also turns out the MCB was upside down, causing mass confusion to the guys on site as it kept tripping out due to only been a "b" type
Earth didnt quite fit in the terminal it seems -
So I isolated the board and made safe and the client agreed to let us install a new fuseboard and sort out the cabling issues!
Found a burnt out lighting circuit then realised this might have something to do with it -
So on with a new DB and enclosure,
I elected for a GRP IP65 enclosure with an eaton TP-N DB inside with all cables + conduits passed through the GRP enclosure with stuffing glands and suitable washers with weather proof glands going into the DB.
New supply for the forklift charger -
Lighting Circuit renewed -
There we have it,
Hopefully they are all up to your exacting standards, and C+C is welcome!