A friend asked me to have a look at a piece of equipment he had recently had installed. It's three phase with an internal transformer (415v to 24v) that provides 24v for the hand switch to operate a relay to switch on the motor. It doesn't work. I measure 8v on the relay rather than 24v. I checked between earth and phase and read circa 150v, I also measure 150V across phases. The motor doesn't run if I manually operate the relay. The three phase is produced via an Allen Bradley device from a single phase supply. The Allen Bradley device is displaying 330 which I take to be a voltage value.The three phase supply is also used for a milling machine that's been working fine for several years and continues to do so. Any thoughts on this. The plate on the milling machine suggests it needs 415v 3 phase. The wiring is dreadful with an isolator being used as a connector block with two outputs one on the switched side and the other confusingly, on the unswitched side so even in off it's on but feeding another isolator which in turn feeds the none functioning machine. The cabling from the Allen Bradley to this isolator is some old twin and earth with little of the outer sleeve. Why do I read 150V both across phases and to earth??
 
What kind of meter are you using?
Like TJ has asked, is the 3ph supply floating?
If you drop off the TX outputs what voltage do you get with nothing connected?
Is the SELV strapped down to earth on one side?
 
Last edited by a moderator:
Hi Darkwood, many thanks, good question. Meter's a cheap old DVM ( I was visiting for free tea). Haven't been back to see if 3ph is floating although wouldn't the phase to phase voltage still read correctly? Voltage didn't change on no load. What would be SELV in this other than the transformer for the relay?
 
Can you draw out a wiring detail so we are all singing on the same hymn_sheet, the way you describe it, it seems --- about face way of doing things, a 1-3PH VSD using the output control voltage and terminal inputs would have been a simpler cheaper way of doing things but it sounds like you have a upfront 1-3phase power converter that then get reduced again for control purposes or am I reading this wrong... remember the voltage output of a motor inverter is subject to the speed setting of the VSD so at half speed the voltage will be approx half. Also to note is the 3ph is generated via pulse width modulation and most digital meters will struggle to read the output voltage correctly.
 
Hi Darkwood, really appreciate your help. The PWM output throwing my meter reading makes a lot of sense as the other piece of kit hanging off this 1-3ph device works OK. I was beginning to doubt my meter. I've possibly confused things mentioning the transformer. Will try and draw it all out.
 
Last edited:

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Eastleigh

Thread Information

Title
Three phase problem
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
6
Unsolved
--

Advert

Thread statistics

Created
Harry_Worth,
Last reply from
Rigpig,
Replies
6
Views
1,070

Advert

Back
Top