A friend asked me to have a look at a piece of equipment he had recently had installed. It's three phase with an internal transformer (415v to 24v) that provides 24v for the hand switch to operate a relay to switch on the motor. It doesn't work. I measure 8v on the relay rather than 24v. I checked between earth and phase and read circa 150v, I also measure 150V across phases. The motor doesn't run if I manually operate the relay. The three phase is produced via an Allen Bradley device from a single phase supply. The Allen Bradley device is displaying 330 which I take to be a voltage value.The three phase supply is also used for a milling machine that's been working fine for several years and continues to do so. Any thoughts on this. The plate on the milling machine suggests it needs 415v 3 phase. The wiring is dreadful with an isolator being used as a connector block with two outputs one on the switched side and the other confusingly, on the unswitched side so even in off it's on but feeding another isolator which in turn feeds the none functioning machine. The cabling from the Allen Bradley to this isolator is some old twin and earth with little of the outer sleeve. Why do I read 150V both across phases and to earth??