LeighSawczyn

Does 6mm2 SWA fit into 25mm Blue MDPE Pipe. The idea being to protect the cable from damp soil or water ingress when it is buried, not for mechanical protection. No tight radii to worry about just a 10-15m straight run.
 
Was questioning to lead the posts the correct way, I don't deal or have experience with HV so would be out of the conversation but if he's talking about running a 6mm 3core to his shed under his back garden then its all usually manual backfill and wouldn't warrant a sheath test as most domestic sparks don't have the appropriate tester to do so, no column on their test sheets for it either... wasn't questioning the testing of the sheath but the circumstances of the install if he's doing a sheath test as this tends to be past your domestic set ups thus curiosity got me, not often a test mentioned on here.

I bet you can drop this conversation into the forum and 90% of the guys who have buried cable on here will not have done a sheath test, I've not done it often myself but thats more to do with the fact I don't bury many cables. I questioned him because of his strange question at the beginning of using a blue pipe as a sheath - its one of them things that ring alarm bells, so had to clarify exactly what kind of install he's doing, he seems to do a test that most on this forum will never have even done yet asks a weird question to boot when standard ducting would be the way to go, even if he had a 10mm clearance he would not get that swa though that pipe as both would have natural bending in them from storage and the friction would be high over 15m length.

@OP - I wouldn't be going anything less than a 50mm duct to drag a 6mm swa through, it will also allow for future issues to be easily rectified if needed to change the cable.

What is the special test equipment? Would you not just use an insulation resistance meter?
 
What is the special test equipment? Would you not just use an insulation resistance meter?

Its the reason I was asking as to what the voltage was and what kind of work he was actually doing, not all sheath teats can be done with a bog standard Insulation test as this is just a 'pulse method', some companies have requirements that mean a 'Time-Resistance method' is the test needed and most of our combi-testers don't have this option and are not designed to say maintain an Insulation test of 500v/1000v DC for 1minute.

The OP gave no indication as to the nature of the work or who he was contracted under and this may well have sent the thread in a totally different direction. I use Time-Resistance method occasionally myself for motor testing during maintenance checks as it has many advantages against the spot reading method and overcomes a few issues that effects your readings.
 
Last edited by a moderator:
And you’re not the most popular person in the world when you tell the cable lads its got to come out.

We would get cable contractors if there were many runs. For the odd runs our quarry production lads were great, they’d done the job many times and really did know what they were doing. Believe me, get them together en-mass and it’s a frightening sight.

They were quite happy with a pull as on Wednesday afternoon as the quarry and crusher shut down for maintenance so the ideal time. A pull was overtime for them plus it was “job and knock”. They got the full afternoon’s overtime and knocked off once the job was done. I dare anyone to tell them the cables got to come out again, your life wouldn’t be worth living.

I've become quite used to being the bearer of bad news, ...at the end of the day it's their work and therefore their problem, not mine!!

We undertake sheath tests after the wet sand fill and allowed to compact around the cable, so not quite as bad as testing after complete backfilling has taken place... lol!!
 
What is the special test equipment? Would you not just use an insulation resistance meter?

I used a bog standard Megger @500V.
You’re not testing insulation as such. You’re ensuring the integrity of the outer serving. We used quarry sand straight out of the washing plant, sopping wet and it soon consolidates around the cable. The damp will soon find its way in to any damage.

The insulation tests Damien mentioned would usually be of five minutes duration, sometimes more for long runs as they take time to charge. Our Megger could read to 100TΩ, 100,000,000,000,000Ω.
It gave one or two some nasty bites. The best one was getting the engineering manager, his own fault for crossing the test area barriers. I’m sat in the substation watching the reading gradually rising when it suddenly shot down and I heard a squeal. Served the silly bugger right.
Others got caught trying to take the leads off before the Megger had discharged the cable.
 
I was a little surprised the first time i ever mentioned the ''Sheath Test'' on the forum, very few had ever heard of the term let alone know how to perform or indeed ever conducted a sheath test. We've since had people here trying to conduct a sheath test with the SWA connected to switch boards etc, and those asking what IR value is acceptable for a SWA sheath test!!
 

Reply to Tight fit or room to spare? in the UK Electrical Forum area at ElectriciansForums.net

Recommended Sponsor News

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top