Hi all
on a TT system, upfront 100mA s type rcd at origin then 5 submains out to 5 small CUs each with its own 30ma rcd main switch
on testing 30mA rcds they are totally fine with upfront RCD bypassed but when tested with upfront RCD installed, all 5 rcd trip early on test
Im thinking this is something to do with the S type RCD test button earth connection maybe?
but why is this effecting the testing of the downstream devices?
all cabling is fine, all high readings
and i have loaded the circuits with as much as i can 10-15A and the rcds are all holding fine, also the Stype is new and testing out fine too
is this an issue thats going to cause potential problems?
Many thanks