Your carrying out an eicr on a domestic property with a time delay 100mA RCD protecting lighting cables within 50 mm of the surface.
What code would you give it c3 or c2?
 
Cables buried less than 50mm from surface require protection by mechanical protection such as earthed metallic conduit ,swa etc or be installed with additional protection by an rcd.
Only a 30ma rcd offers additional protection in this manner.
The OP needs to decide if indeed it's a C2 which is potentially dangerous or C3 requires improvement to make it safer.
 
RCD protection for cables in walls came in with 17th IIRC (?) so if it was built prior and it's in good condition etc then isn't it a C3 at most?
 

Reply to Time delay RCDs and cables in walls in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
380
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
957
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

That is what i am going to do. Thanks mate!
Replies
11
Views
689
  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
957

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top