Dear All
Installation tncs. Wyler re-wireable fuses
I’ve fitted 2 x timeguard rcd sockets to provide protection for extension leads going outside but neither will trip with my tester. Trip fine on test button
Also trip when I do earth loop test ( fluke tester)
Socket tester says it’s all ok
Zs before I changed to rcd socket was 0.45
Doesn’t trip on ramp test
Ze 0.21
What the hell am I missing

Advise appreciated
Cheers
 
Agree with Strima, think you may have an IR fault. Have you done that test? Had similar experiences before, RCD not tripping & RCD tripping on Zs test. Both done to IR fault, neutral earth. That said, that was RCD at origin of circuit, but worth considering.
Yep. IR test done before I started
L/e 180m. L/e 179m. Limited l/n as I couldn’t get to dishwasher or washing machine sockets
 
Agree with Strima, think you may have an IR fault. Have you done that test? Had similar experiences before, RCD not tripping & RCD tripping on Zs test. Both done to IR fault, neutral earth. That said, that was RCD at origin of circuit, but worth considering.
Yep. IR test done before I started
L/e 180m. L/e 179m. Limited l/n as I couldn’t get to dishwasher or washing machine sockets
 
Dear All
Installation tncs. Wyler re-wireable fuses
I’ve fitted 2 x timeguard rcd sockets to provide protection for extension leads going outside but neither will trip with my tester. Trip fine on test button
Also trip when I do earth loop test ( fluke tester)
Socket tester says it’s all ok
Zs before I changed to rcd socket was 0.45
Doesn’t trip on ramp test
Ze 0.21
What the hell am I missing

Advise appreciated
Cheers
Just been informed I’ve reached 100 posts. Does that mean I can attend the electricians arms. Could murder a pint
 
Hi - can I ask which model you're testing? I've seen one that had a weird (to me anyway) separation between the 2 earth connections on the device. If you had that problem your tester would probably not attempt the test, so it's a long shot :)

[ElectriciansForums.net] Timeguard rcd socket won’t trip with tester. Help please
 
Hi - can I ask which model you're testing? I've seen one that had a weird (to me anyway) separation between the 2 earth connections on the device. If you had that problem your tester would probably not attempt the test, so it's a long shot :)

View attachment 41331
Hi Wilkinson
Single is TFA01w
Double is TFA05w
Single only had one earth connection
Double had 2 I think as in a standard double socket
Cheers
 

Reply to Timeguard rcd socket won’t trip with tester. Help please in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
279
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
775
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
783

Similar threads

L
  • Question
My Understanding is the 6 Months interval is IET Guidance and this wording is incorporated onto the label which is a requirement in 514.12.2 where...
Replies
9
Views
646

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top