as from one of my earlier posts, i have been asked to install these fittings if i was to put on a timer would i get 24hr 7 day timer and would this be a straight feed to timer then off to fittings???

cheers trev
 
time clock / contactor

5 linked to 3 / 1

4 / 3

2 / A2

.... / A1 to 2

then 2 on contactor to light Live and 4 on contactor as neutral???
is this correct from my time clock to contactor.


this is rubbish!!!! pay no head .
 
Last edited:
Not sure what you are describing there but sounds like you have 4 as neutral and which will switch with 3, which is connected to 5 and 1 so there is no place for the line to go and you are switching the neutral.
Also A1 and A2 seem to be connected to 2. this does not sound right.
Diagram here of various possibilities for wiring lighting through a timer switched contactor.
[ElectriciansForums.net] timer for lighting 3 x 150w halogen
Not sure which one you are intending to use.
 
grasslin 24hr socket box timer i used and 20A hager contatcor

from spur L to 5 linked 3 to 1 on contactor
N to 4 to 3 on contactor 3 linked to A2 on contactor
2 to A1 on contactor
2 on contactor to L on light
4 on contactor to neutral..
 
grasslin 24hr socket box timer i used and 20A hager contatcor

from spur L to 5 linked 3 to 1 on contactor OK
N to 4 to 3 on contactor Remove 3 linked to A2 on contactor No, link A2 to Neutral
2 to A1 on contactor Need the output from the timer to go to A1
2 on contactor to L on light OK
4 on contactor to neutral. No, remove.

You would short line and neutral with this arrangement.

N to 4 to 3 and spur L to 5 linked 3 to 1 is a direct short L to N
4 to 3 will short out once contactor operates.
2 to A1 means the contactor will only operate once the lights are on, which will not happen because you need to power A1 to turn the light on!
You should remove all neutral connections from the contactor except for one to the coil (normally A2)
Supply the switched line from the timer to A1.


So overall permanent line to 5 and linked to 3 and 1
Line out to lights connected to 2 or 3 or 4
Timed Line connected to A1
Neutral connected to A2

Supply timer and lights with neutral from the neutral supply
 
It is also helpful to wire a Photocell into the coil feed so that the lights only come on if it's dark enough and go off when its gets light in the morning. It is also possible to set the timer for ,say, 2300hrs so the lights go off( if they are not required). This arrangements removes the need to adjust the clock for lighting up time. It can also be used with a PIR so that they only come on if there is an intruder. This will make your brain hurt!!!

Philpot
 
Looking at the timer wiring diagram I realise you may have been referring to numbers from the timer and numbers from the contactor so I have drawn the connections on the timer wiring diagram and a contactor picture, even though Jud has shown it very well this may also help.
[ElectriciansForums.net] timer for lighting 3 x 150w halogen
 
well it is hard to describe fully on internet what i have exactly done, but there must be many ways to wire these contactors. a spark i work with sometimes(aged 45) had drawing me a diagram and i followed and this set up worked.

well it worked via on and off, not setting timer till end of summer.. and i appreciate all your help in talking about what lights etc.. i do i do i do... the drawing is very close to yours richard burns except the neutral is going through 3 on contactor and linked too A2 on contactor.. so i assume breaking the neutral too.???

well first time ive worked with contactor so onwards and upwards just need to know how it functions inside out.. ps got payed and all so happydays and the lights look well. he was abit sketchy about the price but hey ho..
 
Last edited:

Reply to timer for lighting 3 x 150w halogen in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

Thank you for your response. I really appreciate it.
Replies
13
Views
666
I am a landlord/owner of a flat. I am just about to spur off nearby sockets to provide the additional 24hr supply to new Dimplex Quantum storage...
Replies
0
Views
735

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top