Having followed the Power One TL inverter thread I thought I would start a thread covering TL inverters in general.
We have had 2 SMA 4000TL inverters DC Insulation Resistance problems reported this week. One we were out at yesterday and found it was possible to trick the inverter into working by starting with the "good string" and then switching on the "bad string". Having conducted our tests and provided them with our results SMA advised us it was likely to be one of our MC4 connectors so we are in the process of organising scaffolding to carry out the repair.
On to the next one today and as with the one before we were able to identify the "bad string" as our technical customer had also manged to do. He also found the only way to get the inverter to start up when in this state was to start up the "good string" and then witch on the "bad string" when up and running. Now the interesting thing is as it was a bungalow we were able to get up today to redo the MC4's to the "bad string". On coming back down we were able to start the inverter on the "bad string" with no Insulation Resistance fault reported. We then turned on the "good string" and he power increased as expected. All was fine and we felt it was a simple as everyone is suggesting re moisture ingress (despite not actually seeing any evidence of this on the old crimps removed).
Just to check all was well we shut down the inverter and started it with both strings switched on on start up. Then we got the the fault again with the original "good string" now becoming a "bad string". We changed the MC4's took panels off to check connections and then reassembled and all was ok, but from the test we were doing it looked like the DC leakage was dissipating over time as the panels heated up in the sun.
I am now not so convinced that it is the MC4's and beginning to wonder if the fault is somehow linked to the nuisance tripping that the TL's suffer from (when on an RCD protected board) in these damp conditions we have been experiencing recently. Are these same atmospheric condition causing small leakages from the panels as a whole which the TL inverters are designed not to tolerate?
Just a theory at the moment but I am finding anomalies during our repairs that make me cautious of throwing scafollding up when we were able to move the fault from one array to the other today.
We have had 2 SMA 4000TL inverters DC Insulation Resistance problems reported this week. One we were out at yesterday and found it was possible to trick the inverter into working by starting with the "good string" and then switching on the "bad string". Having conducted our tests and provided them with our results SMA advised us it was likely to be one of our MC4 connectors so we are in the process of organising scaffolding to carry out the repair.
On to the next one today and as with the one before we were able to identify the "bad string" as our technical customer had also manged to do. He also found the only way to get the inverter to start up when in this state was to start up the "good string" and then witch on the "bad string" when up and running. Now the interesting thing is as it was a bungalow we were able to get up today to redo the MC4's to the "bad string". On coming back down we were able to start the inverter on the "bad string" with no Insulation Resistance fault reported. We then turned on the "good string" and he power increased as expected. All was fine and we felt it was a simple as everyone is suggesting re moisture ingress (despite not actually seeing any evidence of this on the old crimps removed).
Just to check all was well we shut down the inverter and started it with both strings switched on on start up. Then we got the the fault again with the original "good string" now becoming a "bad string". We changed the MC4's took panels off to check connections and then reassembled and all was ok, but from the test we were doing it looked like the DC leakage was dissipating over time as the panels heated up in the sun.
I am now not so convinced that it is the MC4's and beginning to wonder if the fault is somehow linked to the nuisance tripping that the TL's suffer from (when on an RCD protected board) in these damp conditions we have been experiencing recently. Are these same atmospheric condition causing small leakages from the panels as a whole which the TL inverters are designed not to tolerate?
Just a theory at the moment but I am finding anomalies during our repairs that make me cautious of throwing scafollding up when we were able to move the fault from one array to the other today.