I recently completed a report on an exsisting Installation - TN-C-S Two 400mm SWA Supply cables with 185mm Earth and 1250A ACB
Reading of Ze was 0.22 ohms. Although not over the maximum permitted it means all Zs readings for submains circuits ARE over the maximum permitted. The smallest submains circuit on site is a 100A MCCB which has a maximum of 0.18 ohms, which is already nearly above the reading of Ze. All other submains are 200A & 315A.
i was quite surprised that the Ze reading was so high given its a TN-C-S and the size of the supply cables. It was however obtained when the factory was in full production and could not be turned off or main earth disconnected. That is the next step to get the true reading of Ze and if above will be the supply companies problem. However if the Ze does increase but not above 0.35 ohms is it acceptable to install rods, increase bonding conductor size to steel etc to reduce the general reading of Ze. I doubt the client will wish to install earth leakage devices at mains ACB and/or submains MCCB and I also don't believe the MCCBs are adjustable