TN-C-S? No, TN-S. | on ElectriciansForums
Discuss TN-C-S? No, TN-S. in the UK Electrical Forum area at ElectriciansForums.net
HandySparks
Mentor
Hampshire
Thought this might interest some. Doing a CU change. Took a quick look at the supply head, saw the earth terminal on the side and assumed TN-C-S. When the chap from EDF turned up to change the meter and connect to my isolator, it turned out to be TN-S. It looks like the underground supply cable is split concentric; you can see the black insulated strands to the neutral terminal and bare copper to the earth terminal.
Ze was 0.17ohm, Z line was 0.18ohm, so testing wouldn't really have revealed what the earthing arangement was. By the way, does anyone know if there's a standard symbol for the line impedance, line to neutral?
[ElectriciansForums.net] TN-C-S? No, TN-S.[ElectriciansForums.net] TN-C-S? No, TN-S.
Although they don’t use split concentric now, something sticks in my mind about them using it around that time. we were told about it at EMEB’s training collage, they stopped using it due to the outer serving and neutral insulation getting damaged leaving a TN-C-S connection in effect.
I could be wrong about them using it U/G. It was something that was stuck in the back of my mind from EMEB 20+ years ago.
Don't reckon your far off mate, I have seen it fed in ducts before (from ryefield) between these little bungalowish sort of things at a 'scheme' for mentally ill people. I bet theres a few like it but you never see them as most people would assume PME seeing a concentric and a PME style cutout.
Reply to TN-C-S? No, TN-S. in the UK Electrical Forum area at ElectriciansForums.net
A bit like saying plumbers makes good electricians. 🥴
How did it go?