Hi everyone,
Just wanting to confirm something, could you please let me know if these pictures are describing a TN-S or TN-C-S system?
Thanks in advance
 

Attachments

  • [ElectriciansForums.net] TN-C-S or TN-S?
    IMAG0574.jpg
    71.4 KB · Views: 244
  • [ElectriciansForums.net] TN-C-S or TN-S?
    IMAG0558.jpg
    95.3 KB · Views: 241
I would say they are both TN-S systems to be honest, though the one on the right as a sticker next to the earth terminal, which I can't read., which sometimes denotes a TNC-S.

Best way to test, Ze and if you have a low reading below 0.20ohm then most likely TNC-S anything above 0.35 and then I would go for TN-S

You can also do a PEFC and a PSCC test and if they are basically the same you will have a TNC-S
 
They both appear to be TN-S as the main earthing facility is via the suppliers cable sheath.

Although pic 2 does not appear to have a main earthing conductor attached to the MET adjacent to the supply cable???
 
Thanks for your reply, I thought they were TN-S too. But in the 2nd picture it's a customer's house where they had no earth, so we requested the DNO put in a
PME, which they did, and a PME is described as Protective Multiple Earthing System, which sounds like a TN-C-S? and this picture is showing the situation after a PME was put in.
So I'm not sure now, which is why I decided to ask you guys.
Thanks
 
The 1st picture is showing a previous job I did, and I thought that was a TN-S and then I came across this second job and that's a TN-C-S system, and from what I understand, both these systems are the same they look like the same thing is happening, could you please explain how I can tell they are different? I would appreciate that.
 
I would say they are both TN-S systems to be honest, though the one on the right as a sticker next to the earth terminal, which I can't read., which sometimes denotes a TNC-S.

Best way to test, Ze and if you have a low reading below 0.20ohm then most likely TNC-S anything above 0.35 and then I would go for TN-S

You can also do a PEFC and a PSCC test and if they are basically the same you will have a TNC-S

Thanks for your reply,
First picture: Ze 0.32, PEFC 1kA
 

Reply to TN-C-S or TN-S? in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
295
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
804
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
839

Similar threads

so Ze 0.35Ohms and my Part of the Circuit just half of R1+R2 is 0.19353Ohms as its 1.5mm x 10m so well under but dont know of any switch gear...
Replies
6
Views
1K
FFS - popped it apart, found the same issue and thought I'd update... You guys were already there!
2
Replies
21
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top