P

P&Q

Hi everyone,
Just wanting to confirm something, could you please let me know if these pictures are describing a TN-S or TN-C-S system?
Thanks in advance
 

Attachments

  • IMAG0574.jpg
    IMAG0574.jpg
    71.4 KB · Views: 252
  • IMAG0558.jpg
    IMAG0558.jpg
    95.3 KB · Views: 249
The sheath could be connected to the neutral in the head, so could quite conceivably be TN-C-S. I've seen them do this a couple of times where the sheath on the PILC has lost it's earth connection somewhere, so they've joined the two and at the same time maintained the protection the sheath gives.

They wouldn't label it for nothing.
 
Having spoken to a local jointer, they will never supply TN-C-S through PILC except under certain circumstances such as that outlined above (and even then only if certain conditions are met), and they will always use 4 core cables in the street where houses are supplied by PILC, so it is most likely TN-S.
 
Last edited:
They are both TNS if it was a pme it the dno would not use earth braid they would use 16mm cable that is sheathed. If this was a pme then that braid would be an exposed neutral conducter
 
TNS , word of warning chaps when testing your Ze on what looks like a TNCS with the earth block on the side of the cut out , switch off the supply disconnect all main Earth and main bonds and then test across the in terminals of the isolator and the earth block this will confirm that the earth block is connected to earth either TNCS or TNS , reason i say this is over the past few month i have come across the same error in connecting the earth to an unconnected cut out earth block , the one i recently did looked like a TNCS but was infact a TNS with the original earth cut off , the earth was reconnected by the DNO with the earth running into the cutout and to the earth block ,
 
The Ze reading is no reliable indication of whether it's TN-S or TN-C-S, IMO. There is a large 60's estate near me where every house is a TNS. There are sub-stations sprinkled across the estate and I've got Ze readings between 0.08 and 0.23 in various houses.
This is the cutout fitted in these houses:
TN-S not TN-C-S - Shared photo album - PhotoBox

That would have fooled me, i would definitly have taken that cut out to be a PME supply!!!
 
The Ze reading is no reliable indication of whether it's TN-S or TN-C-S, IMO. There is a large 60's estate near me where every house is a TNS. There are sub-stations sprinkled across the estate and I've got Ze readings between 0.08 and 0.23 in various houses.
This is the cutout fitted in these houses:
TN-S not TN-C-S - Shared photo album - PhotoBox

I have also come across several of these types of service heads years back. The cable coming in is a three core and the head has three separate chambers within it. It taught me never to assume TN-C-S just because the earthing conductor came from the head. Similar PSCC and PEFC readings seemed to work for me to confirm TN-C-S systems.
 

Reply to TN-C-S or TN-S? in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
175
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
1K
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

  • Question
Yes Table 3A that was in Appendix 3 of the 17th edition of BS7671 and in BS 7671:2018 (Blue Book) up to the release of BS7671:2018 +A2:2022 (Brown...
Replies
11
Views
1K
FFS - popped it apart, found the same issue and thought I'd update... You guys were already there!
2
Replies
21
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top