Came across this on a rewire, looks to me like a TN-C-S, but had SNE on the side as you can see, we thought as the sheathing was metal it could mean (seperate neutral & earth) and be a TN-S, never seen before and could just be coincidence, a point in the right direction would be handy, cheers.
 

Attachments

  • [ElectriciansForums.net] TN-C-S or TN-S ???
    image.jpg
    215.6 KB · Views: 154
Clearly I agree they are different but in a PME system both the Ze and the PSCC will be almost identical measured as I mentioned in my 1st post, and more than likely different in a TN-S setup.

You agree?
No , In a PME system both PEFC and PSCC will be identical, NOT Ze and PSCC !!! where on earth do you guys get this from????
Tell me,what is the relation between Ze, PEFC and PSCC ?? Please come on guys
 
Ze = external loop impedance(measured between L-E on incoming side, with E disconnected) PEFC = Prospective earth fault current (Uo/Ze L-E) PSCC = Prospective short circuit current (Uo/Ze L-N) measured on load side with all conductors connected
hope this clears it up
 
No , In a PME system both PEFC and PSCC will be identical, NOT Ze and PSCC !!! where on earth do you guys get this from????
Tell me,what is the relation between Ze, PEFC and PSCC ?? Please come on guys

I am not saying that the readings for Ze and PSCC will be the same as they are measured in Ohms and KA respectively, I am saying that if you test as I said in my original post that in a PME system if you measure Ze with prongs to L, N and Earth you will get the same reading in Ohms as you would connecting you L prong to L and your N and Earth prongs to N............if the results are different then it will be TN-S.

I am not disagreeing with your comment i just feel mine is also correct.

Surely the relationship between Ze and PSCC is V=PSCC*Ze

i.e. If PSCC=0.96 KA and Ze=0.25 Ohms then V=240 Volts.....................Right?
 
Ze = external loop impedance(measured between L-E on incoming side, with E disconnected) PEFC = Prospective earth fault current (Uo/Ze L-E) PSCC = Prospective short circuit current (Uo/Ze L-N) measured on load side with all conductors connected
hope this clears it up

Cut the crap Marnik's right and it's pme , tns cable reported with with high values converted to pme!
 

Reply to TN-C-S or TN-S ??? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
274
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
269
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
350

Similar threads

  • Question
A bit like saying plumbers makes good electricians. 🥴
Replies
10
Views
2K
  • Question
You need a CT clamp at main tails, it depends on the rules where you are - you used to be allowed wireliss ones (such as MyEnergi Harvi), these...
Replies
14
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top