Which regulation do you believe requires this? It helps us to help you if you answer this. If you don't know, just say so.
See BS7671 definitions: "fault protection".
411.4.5 permits either an RCD or overcurrent device for fault protection.
An RCBO is both an RCD and overcurrent device.
We are looking for a maximum permitted Zs for the B16 30mA RCBO.
See dictionary definition :"maximum"
Table 41.3 offers a maximum Zs for the overcurrent part of a B16 RCBO of 2.73 ohms.
Table 41.5 offers a maximum Zs for the RCD part of a B16 30mA RCBO of 1667 ohms.
Of the two values, 1667 is higher, and is permitted by 411.4.5. Therefore 1667 is the maximum permitted Zs for a B16 30mA RCBO to BS61009.
I am not interested in playing the regulation game, maybe some other day Lets stick to BS7671 and ignore legalities as it is not relevant to my original post.
Generally agree with what you have stated here. However I would disagree with your conclusion.
I would say of two values, 2.73 ohms is lower than 1667 Ohms and as Table 41.3 mandates a max 2.73 ohm Zs we can not exceed this value as to do so would result in BS7671 non-compliance for overcurrent characteristics of RCBO.
What you are doing is applying Table 41.5 and ignoring Table 41.3. For BS7671 compliance the full standard has to be adhered to in it's entirety.
If you disagree, please elaborate.