TN-CS or TNS? | Page 2 | on ElectriciansForums

Discuss TN-CS or TNS? in the UK Electrical Forum area at ElectriciansForums.net

W

wcampbell

Hi all.

Can someone tell me what kind of E system this is?

I think its TNCS but the 6mm to E Sleeve is confusing me.

I think the MET is connected to the N - hence TNCS.

Should I upgrade 6mm E.

Thanks for your replies.
 

Attachments

  • [ElectriciansForums.net] TN-CS or TNS?
    electrics 002.jpg
    139.7 KB · Views: 242
That piece of cable as Telectrix points out, be it 4, 6 or 10mm, IS the fuse. Its protective device is the suppliers fuse which will only pop with a large current flowing, well after that piece of cable has melted/caught fire.

Hard to know what else to say really its been suggested already, maybe get someone in to do it and watch.

Saying that, it might be a 60A fuse but its still a demonic mess
 
Last edited by a moderator:
700a x 5s / 115 = 13.5mm = 16mm needed.


​if that's supposed to be an example of the adiabatic equation, then i suggest you do some reading.
 
Thanks for all the replies.

I let a Sparky with some forty years experience connect Sub Main Cable at the origin of the circuit ( although he did send someone else to do it ).

My experience may be low but I'm learning at a great rate of Knots.

On Friday I isolated Sub Main at origin with 63a Rcd. The RCBO in extension DB has 100a Isolator.

The Line Conductor cable has a CSA of 6mm so that's 12mmsq.

The time/current graphs in Regs say 100a RCBO = 500amps.

500x5/115 = 9.72.

Going to run 10mmsq from extension DB to MET at origin of the circuit.

I never gave a thought to the work done at origin, why would I - it's been done by a qualified Spark!
 
as previous poster said, are you sure your ready to be assessed? not having a go like but anyone with any elec experience would see that the wiring on that meter is a lash up,do yourself a favour mate seriously get more experience,how are you gonna do the job if you don,t know when something isn,t done right?
 
Thanks for all the replies.

I let a Sparky with some forty years experience connect Sub Main Cable at the origin of the circuit ( although he did send someone else to do it ).

My experience may be low but I'm learning at a great rate of Knots.

On Friday I isolated Sub Main at origin with 63a Rcd. The RCBO in extension DB has 100a Isolator.

The Line Conductor cable has a CSA of 6mm so that's 12mmsq.

The time/current graphs in Regs say 100a RCBO = 500amps.

500x5/115 = 9.72.

Going to run 10mmsq from extension DB to MET at origin of the circuit.

I never gave a thought to the work done at origin, why would I - it's been done by a qualified Spark!

Son I do really try to help people on here, and I'm all for people learning .......but to be honest your clueless and you are a danger to yourself, and to anyone else you decide to do electrical work for.

Please do not take that assessment, I don't know what training you had or if your still in training or whatever, but please rethink you do not have the skills or training to be assessed and then take work on in peoples home.

Blunt, yes it can be, but I'm worried for your and others safety
 
If I were in your shoes I would seriously consider following the advice of these respected members.

The appropiate action would be to contact the assessor as soon as or before he arrives, if not still meet him at the clients address or if its your address, better still!

Explain you cant go head with your assessment and admit you have bitten off more than you can chew and that the assessment is too complex based on your experience and knowledge, therefore you have identified your limitations and he may more than likely respect you as you have identified your limitations as a practicing electrician. He may want to look at the installation and agree with you that it is out of your scope. If he does agree then he will ask you to book the assessment another time using a lot less complex installation. The only thing he maybe annoyed about is travelling there, thats if he's travelled far.

What makes a godd electrician/competent electrician is someone who knows there limitations and is willing to seek help and guidance.

WAMS
 
It's too late to cancel the assessment so you might as well go through with it. But do not be surprised if the assessor fails you. If you are really lucky he may ask you to put right certain things and provide proof it has been done. Either way you can expect a lot of questions from the assessor.

You seem to have a bit of electrical knowledge but judging from your comments and descriptions you are not yet competent. You need to either go (back?) to college or get an experienced electrician to let you work with them. We're not trying to put you down, we're just giving you a fair assessment of your current abilities. Do not be discouraged, but you need to learn some more.

Sent from my HTC Sensation using Tapatalk
 
Hi all.

Can someone tell me what kind of E system this is?

I think its TNCS but the 6mm to E Sleeve is confusing me.

I think the MET is connected to the N - hence TNCS.

The values of your Prospective Fault Currents should give you a good indication of which earthing system it is.

Hope your assessment isn't too much of a nightmare!
 

Reply to TN-CS or TNS? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
301
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
813
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
869

Similar threads

  • Question
Yes, for example: https://kingsmillindustries.com/product/km2-20-10-sc/ However, the reality is the L-N-E style are far more useful in general as...
Replies
2
Views
973
  • Question
Generally speaking local earthing will rarely be below a couple of ohms, so in parallel with a TN-S sub-ohm value will make little difference...
Replies
4
Views
695

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top