Evening guys,

I`m doing a small commercial job involving 2 x 3 Phase boards. The secondary board is 15 meters from first and is gonna supply up to potentially four 3 phase machines plus a ring main supplying portable single phase equipment.

Help sizing the supply cable for the second DB. Not used to dealing with start up currents etc. Here is a list of the max amount of equipment to be used. This is info customer has given to me.

Planer: 3 phase, 1.5 Kw, Full Load 3.6A, starting current 21.6 A

circular saw: 3 phase, 4 - 6 Kw, (other details unavailable)

Chopsaw: 3 phase or single, 2 - 3 kw

pillar drill: 3 phase or single, 1 - 2 Kw

Lathe: 3 phase, 3 - 4 kw

bandsaw: single phase, 2 - 3 kw

mortiser: single phase, 1 - 2 kw

cheers
 
top of my head, you want around 25kW over 3 phases, say 9kw/phase, thats 40A. allow for inbalance , my poor guesswork, and future expansion, gives 10mm on a 63A type C. as a starter for 10. now work out Zs values and disconnection times.
 
Last edited:
All wiring is surface, so am I right in saying that only circuits supplying portable equipment would need to be on RCD or would it just be easier to put everything on RCD?
 
would I continue with a 16mm/sq earthing conductor to the second db or would 10mm do?
you need to do the calcs. to decide. remember that the max. Zs for C type breakers is 1/2 what it is for type B.
 
Are any of the D.B's already in situe or are you designing the full install?, avoid subbing the second board off the first as you will not get discrimination, if you have a short on any of the DB2 circuits it may take out a 63amp mcb before say a 10amp downstream.
 
All wiring is surface, so am I right in saying that only circuits supplying portable equipment would need to be on RCD or would it just be easier to put everything on RCD?
if your on about the proposed ring final serving these points for your portables...then by all means provide additional protection....but the other stuff?...skilled and/or instructed person/s....and also surface run......
 

Reply to Tn-s 3 phase? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
438
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Just stick the 63amp fused connector before the Henley block , or Lucy block as you call it, and your all good, as for your 2nd point, , the...
Replies
1
Views
1K
When I was on the electric board We had a pair of pillocks connect a housing estate to a very large genset, the n lead was in two parts and not...
2
Replies
28
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top