I'm interested in collating the differences in the requirements (not the definitions) between TN-S and TN-C-S.

I've aleady seen an example in another post tonight: "TN-S Ze max is 0.8", Any other quotes (with regs reference if possible)?
 
TNCS not to be used in many special locations
What special locations are you talking about.I have a TNCS at home.I have a swimming pool and a sauna:rolleyes:And a yacht moored up in the marina at the bottom of my garden
 
Last edited by a moderator:
Not BS7671, but ESQCR...DNO tend not to allow exportation of TNCS earth. Some do allow say two metres outside equipotential zone. Generally, from experience, they seem to be ok with exporting TNS earth.

Yooj
 
Last edited by a moderator:
708.411.4= TN-C-S not permitted in caravan parks or similar

709.411.4= TN-C-S not permitted for supply to boat or similar

711.411.4= TN-C-S not permitted for exhibition stands or similar

717.411.4= TN-C-S not permitted for mobile or transportable units

721.411.4= TN-C-S not permitted for supply to Caravans
 
I'm interested in collating the differences in the requirements (not the definitions) between TN-S and TN-C-S.

I've aleady seen an example in another post tonight: "TN-S Ze max is 0.8", Any other quotes (with regs reference if possible)?
TNC-S. As everyone knows, the customer is provided with a connection to the System Neutral to use as their main earth. The Neutral will be earthed at the star point of the supply transformer, again at the end of the main, at or beyond the connection of the furthest customer on that cable. In addition, earths are added to the neutral along the main at appropriate points, to reduce the System Neutral to earth potential under normal conditions, and to limit the potential on the System Neutral compared to earth in the event of a break occurring on the Neutral conductor back towards the supply transformer.

With TNS, the star point of the supply transformer is earthed. A separate conductor is provided back to the supply transformer to connect to the customer's earth transformer. Virtually all TNS supplies are provided on lead mains, the lead sheath / steel armouring effectively acts like a large earth rod, equivalent to the length of the cable.

With TT, the star point of the supply transformer is earthed. No earth connection is provided to the customer
 
That looks a bit familiar too!^^^


Original Post by me -


Ok mate here goes.

We are all used to TT, TNS and TNC-S as supply types.

I'll start with TNC-S. As everyone knows, the customer is provided with a connection to the System Neutral to use as their main earth. The Neutral will be earthed at the star point of the supply transformer, again at the end of the main, at or beyond the connection of the furthest customer on that cable. In addition, earths are added to the neutral along the main at appropriate points, to reduce the System Neutral to earth potential under normal conditions, and to limit the potential on the System Neutral compared to earth in the event of a break occurring on the Neutral conductor back towards the supply transformer.

With TNS, the star point of the supply transformer is earthed. A separate conductor is provided back to the supply transformer to connect to the customer's earth transformer. Virtually all TNS supplies are provided on lead mains, the lead sheath / steel armouring effectively acts like a large earth rod, equivalent to the length of the cable.

With TT, the star point of the supply transformer is earthed. No earth connection is provided to the customer.

Both have disadvantages TN-S for instance - if the sheathing of the cable breaks down this could go un-noticed for years as the bonding conductors would be providing a paralell path to earth. You would know straight away if a TN-C-S conductor was lost.

Most DNO's stste that anyone on TN-S should be "upgraded to TN-C-S as TN-S is no longer supplied on new installations

Take a look at the link below aswell.


Hope this helps.


http://---------------/Publish/WireR...s_answered.pdf
 
Last edited by a moderator:
Although you are correct in the basic differences and pros and cons between TN-S and TN-C-S there are inherent dangers with TN-C-S if not correctly used, that is not to be used on restricted installations as as defined by the ESQCR or where correct sized main equipotential bonding is not used or equipotential zones are not established for example in a garden with metal fittings where there may be a potential difference between the neutrally earthed conductive parts and and ground earth.

In the rare circumstances where a service PEN conductor is severed on its own then it is not always obvious in the installation, where bonded steelwork is providing a low resistance earth path this will act as a neutral, this is the reason for the larger csa of main bonding conductors now

In the early 70`s I was an intallations inspector when PME first appeared, 2.5sqmm was the minimum size, this caused more than one property to burn on an estate in Romford when network current tried to use the bonding via metal water services as a neutral after a network neutral was severed on the overhead lines

TN-C-S is used primarily for economic reasons by DNO`s however it does provde a lower Ze than TN-S in most cases

So used properly by good electricians TN_c_s is no problem, used by DIY or our John Wayne friends, not so good
 
That looks a bit familiar too!^^^


Original Post by me -


Ok mate here goes.

We are all used to TT, TNS and TNC-S as supply types.

I'll start with TNC-S. As everyone knows, the customer is provided with a connection to the System Neutral to use as their main earth. The Neutral will be earthed at the star point of the supply transformer, again at the end of the main, at or beyond the connection of the furthest customer on that cable. In addition, earths are added to the neutral along the main at appropriate points, to reduce the System Neutral to earth potential under normal conditions, and to limit the potential on the System Neutral compared to earth in the event of a break occurring on the Neutral conductor back towards the supply transformer.

With TNS, the star point of the supply transformer is earthed. A separate conductor is provided back to the supply transformer to connect to the customer's earth transformer. Virtually all TNS supplies are provided on lead mains, the lead sheath / steel armouring effectively acts like a large earth rod, equivalent to the length of the cable.

With TT, the star point of the supply transformer is earthed. No earth connection is provided to the customer.

Both have disadvantages TN-S for instance - if the sheathing of the cable breaks down this could go un-noticed for years as the bonding conductors would be providing a paralell path to earth. You would know straight away if a TN-C-S conductor was lost.

Most DNO's stste that anyone on TN-S should be "upgraded to TN-C-S as TN-S is no longer supplied on new installations

Take a look at the link below aswell.


Hope this helps.


http://---------------/Publish/WireR...s_answered.pdf
Hi Lenny,must have found it on the same link you did:D
 

Reply to TN-S vv TN-C-S in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
267
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
762
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
752

Similar threads

FFS - popped it apart, found the same issue and thought I'd update... You guys were already there!
2
Replies
21
Views
2K
I can't help wondering about earthing arrangements and how important aesthetics really are when attempting to make the best of a less than ideal...
2
Replies
21
Views
1K
nicebutdim
N

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top