Ok mate here goes.
We are all used to TT, TNS and TNC-S as supply types.
I'll start with TNC-S. As everyone knows, the customer is provided with a connection to the System Neutral to use as their main earth. The Neutral will be earthed at the star point of the supply transformer, again at the end of the main, at or beyond the connection of the furthest customer on that cable. In addition, earths are added to the neutral along the main at appropriate points, to reduce the System Neutral to earth potential under normal conditions, and to limit the potential on the System Neutral compared to earth in the event of a break occurring on the Neutral conductor back towards the supply transformer.
With TNS, the star point of the supply transformer is earthed. A separate conductor is provided back to the supply transformer to connect to the customer's earth transformer. Virtually all TNS supplies are provided on lead mains, the lead sheath / steel armouring effectively acts like a large earth rod, equivalent to the length of the cable.
With TT, the star point of the supply transformer is earthed. No earth connection is provided to the customer.
Both have disadvantages TN-S for instance - if the sheathing of the cable breaks down this could go un-noticed for years as the bonding conductors would be providing a paralell path to earth. You would know straight away if a TN-C-S conductor was lost.
Most DNO's stste that anyone on TN-S should be "upgraded to TN-C-S as TN-S is no longer supplied on new installations
Take a look at the link below aswell.
Hope this helps.