Does the DNO change TT systems into tncs by changing the head to a tncs cut out and providing met? The Ze I measured was 0.60 and when main earth reconnected reding of 0.40 on the met . There is an earth electrode and 30 mA rcd as a main switch . Is this a TT system or tncs ?
 
There is an earth electrode and 30 mA rcd as a main switch . Is this a TT system or tncs ?

dont know whats goin on in the rest of your post but this^^^ is indeed a TT system.
the MET is always fitted / supplied by the consumer but a modern tncs cutout will have an seperate earth terminal , usually linked to the neutral.
 
Does the DNO change TT systems into tncs by changing the head to a tncs cut out and providing met? The Ze I measured was 0.60 and when main earth reconnected reding of 0.40 on the met . There is an earth electrode and 30 mA rcd as a main switch . Is this a TT system or tncs ?

You need to ask the DNO out to make some measurements and if Ok provide TNCS (PME).
 
TT system is a stake in the ground providing an earth and R.C.D. providing protection.
p.m.e. is earth and neutral on same block and readings over 0.35ohms are considered to high and should be reported to supplier (EDF etc) and if p.m.e. is available it should have a note on or near cut out stating p.m.e. is available. some old tn-s systems sometimes have earth block on side of head so look like tn c-s
sorry if ive just told you how to suck eggs.
hope helped.
ta kipper
 
The DNO have been replacing the old meters. When they do they upgrade the head to allow for a PME if possible.

But its not a PME unless the consumer gets an electrician in to make it so.

It sounds to me that you have the potential for PME but are still using an earth electrode.
 
The DNO have been replacing the old meters. When they do they upgrade the head to allow for a PME if possible.

But its not a PME unless the consumer gets an electrician in to make it so.

It sounds to me that you have the potential for PME but are still using an earth electrode.

In most European countries, they insist on a local, ''on premisses'' earth rod. It should be a condition of supply in the UK too. It'll certainly reduce the effects of a broken or high resistance neutral problems on the main distribution cable....
 

Reply to Tncs or TT ? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
303
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
284
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
356

Similar threads

  • Question
I'm assuming the cable will have to be cleated well to hold it in place anyway, as a stuffing gland ain't going to hold it tight like a SWA gland...
Replies
10
Views
676
  • Question
Generally speaking local earthing will rarely be below a couple of ohms, so in parallel with a TN-S sub-ohm value will make little difference...
Replies
4
Views
677

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top