TNCS Service head, earthing and bonding | Page 2 | on ElectriciansForums
Discuss TNCS Service head, earthing and bonding in the UK Electrical Forum area at ElectriciansForums.net
Essex
Went to quote for customer's dis board upgrade today found this gem! looks like 6mm main earthing, main bonding etc going into the MET within service head.. also no plastic case on head. I presume I would contact DNO to resolve and provide 16mm + additional MET? Just haven't come across this yet.
There are other big issues with the installation that are obvious so quoted for EICR previous to DB change. Also don't fully understand why there are two meters still as DNO fitted digital one only a few years ago? I think the other one is redundant as can't see what its supplying... there has never had a rented area within the property to justify another meter..
thanks
[ElectriciansForums.net] TNCS Service head, earthing and bonding
Could that DNO cut out be TN-S and not TN-C-S as OP suggest. I'm just wondering if there is a link under the plastic cover which shorts out the neutral and earth block for PME. At the end of the day test will confirm which system used.
Reply to TNCS Service head, earthing and bonding in the UK Electrical Forum area at ElectriciansForums.net
If it's buried ducting, have you thought about digging up a section of the buried cable close by, cutting it and pulling in a few extra meters...
In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...
Recommended Sponsor News
Hi everyone,