Just a general question, how is it when we touch live to earth or there is a short circuit between live and neutral there is an electrical explosion or some sort of reaction however when we use a tncs earthing systems should this not happen as the earth & neutral are combined therefore any return current in the neutral will short with earth, would appreciate it if anyone could explain the theory of this haha?
 
A "Load" has a resistance, Earth is the fault path and has very little resistance. Low resistance=100+ amps flow.
You Protective device will only allow a certain amount of current to flow, Thus it disconnects.
You have have a fault between line and Netural(or CPC) you miss the load out IE the current takes the easyest path "pop" MCB goes.
 
you get the flash due to the high current caused by a low resistance short. as both the N and E are at 0v, nothing happens if N and E short, but shorting L to either will give rise to a large current, causing flash and bang due to nthe conversion of electrical energy to sound and light.
 
Firstly a definition of short circuit: The coming together of two conductors of differing potential with minimal impedance. Now, between Line and Neutral there is a potential difference of 230V in your house. Likewise, between Line and Earthing conductor there is a potential difference of 230V. But, between Neutral and Earthing conductor there is usually no potential difference and being at the same potential cannot result in a short (or any) circuit. Hope this helps too.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Back
Top