Went to look at a job on Friday and I think I already have the answer just putting it out there.
Factory has been completely gutted been asked to put in a 315a TPN by the head running a sub main to the other part of the building they are going to be using.
My problem is I already have a Ze of .26 then when I add on the cable run it is going to be well over the .14 maximum zs allowed. Apart from putting in an rcd unit what (if any because I can't think of any) other options do I have?
Client is really not happy with the thought of rcd on the submain even tho I have explained it would be time delayed etc etc and they would never even know it was there.