Have you carried out a Ze at the boards.
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss TNS in the Commercial Electrical Advice area at ElectriciansForums.net
A couple of months ago yes when it was first powered up..As far as I remember it was around 0.07..(quite big job over a hundred DBs so not sure)Have you carried out a Ze at the boards.
No continuity on an accessory fault traced to defective modular kit.faulty circuit disconnected (I think)unless labled wrongly.not confirmed yet.What is the nature,of the fault?
One or the other...manual changeover.Are both A & B supplies used at the same time or is it a duty / standby situation?
Thank you...For the Neutral Earth loop on the installation you describe the 0.03Ω sounds about right (as Wilko has just said!)
So the A installation sounds correct but the B does not.
View attachment 39394
Therefore the neutral of the non operational supply (B) is probably not connected to your live supply as this would mix the two systems of the supply transformers.One or the other...manual changeover.
Thank you...
Both supplies are operational..voltage to earth is 240 on both systems..There is some info about earthing neutrals through impedences(fig 44.1)and section 442 .not too clear to me..Therefore the neutral of the non operational supply (B) is probably not connected to your live supply as this would mix the two systems of the supply transformers.
Hi.I cant really comment.I will need to investigate further.The complex has 5 sets of HV/LV Transformer rooms(Subs) (Times 2 :A+B) I believe there are two independant 11,000volt ring mains.They wont let us doe_heads in to the substations.Hi,what is the set-up,regarding the two supply transformers,and what is feeding them?