Evening all,

I as doing a new kitchen install today, and noticed that the main incoming water supply is done in plastic.

The stopcock and pipes running out to an outside tap are in copper however.

I was wondering if it is wise to introduce a potential difference by bonding the copper sections, but the surrounding circuits in this area are rcd protected so no supplementary bonding required.

I have attached a pic, this seems to be a grey area.

Thanks in advance.
 

Attachments

  • [ElectriciansForums.net] to bond or not to bond?
    WP_000044.jpg
    75.8 KB · Views: 95
Looking at it, it's highly unlikely that you'll be needing any main protective bonding.
The leg to the tap should certainly NOT be bonded and is often fitted with a plastic insert to isolate any bonding that is required.

The kitchen is not a special location so would not need supplementary bonding anyway.
 
Quite simply, no.
If it was a requirement to bond that set up then we'd have to bond every installation in the land, that should be a delight to see for every electrician.
I bet you ain't as lucky with the gas though.
 
Just test between the MET and the incoming service, and if a reading greater than 23k ohms no need to bond. If less, needs bonding to bring to the same potential.... I.e less than 0.05 ohms.
Simple to do, and a guaranteed method.
GN8.
You will find a lot of services don't need bonding, as they are not a parallel path to earth.
Hope this helps
 

Reply to to bond or not to bond? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
382
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
963
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
4-5 hours for 150? no chance, this is 2024, 150 for 2 hours maybe, that said an hour seems pretty quick, not sure he did the job right
2
Replies
23
Views
2K
  • Question
There could also be a completely unsuitable junction box embedded within the wall and tiled over or just cables in choc blocks in old accessory...
Replies
6
Views
994

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top