hi guys I'm testing a elderly peoples home I have all the correct readings on the ring mains however they are on a 32amp 60898 type b mcb should I grade as c2 or c3 or can it just be passed as satisfactory
 
hi spinks yes mate theres all sorts of equipment hospital type movement beds / Kitchens although all bonding in place in special locations etc. also 3phase board no rcd protection
 
Last edited by a moderator:
Coding would depend on the use of sockets,if they might reasonably be expected to supply equipment outdoors for example, a C2 might be appropriate,otherwise a C3

Edit...I'm assuming the OP is concerned about RCD protection,as Murdoch states though,thats not made clear.
 
Hi Murdoch I was only coding it as I though that it does not comply to current regs as you rightly say everything has tested ok, there is no sockets used externally ie grounds maintenance etc back to the original post satisfactory or unsatisfactory ?
 
What you need to look at is what the socket is used for and its risks, elderly people home could have breathing machines dialysis machines etc ,you don't really want them on an RCD if you take into consideration the disconnection time 0.4 and Zs required to trip the protective device in that time , if the test result are within the required levels then no code if higher then there might be an underlying problem , you could code 3 it requires improvement , assess the level of risk really RCD's are for additional protection
 

Reply to to fail or not to fail in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
514
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
2K

Similar threads

I usually put something like this To assess compliance with BS7671 for continued safe operation (5 year periodical inspection)
Replies
8
Views
471
  • Question
When I did my AM2, I had it drummed into me that I had to follow Guidance Note 3 carefully. So, did you follow the guidance in GN3 for checking...
Replies
1
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top